Yes they are similar and essentially represent the same thing. The sign convention is opposite of each other because one describes heat flow toward the “inside face” and the other toward the “zone air”. The values do differ slightly because of how the numerical solution works out. The Zone Air Balance version is somewhat more exact as it is based on the solution’s result for zone air temperature and is calculated only for reporting. The Surface version is used to feed into the calculation of the zone air temperature and for numerical reasons it ends up using a lagged value for the zone air temperature (from the previous timestep). From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Yan Xue Dr. Li __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.