[EnergyPlus_Support] how to control nominal Capacity of Coil:Cooling:Water??



I can't control my cooling coil 
Given this data how can i calculation nominal capacity of the coil?
The total capacity should be 468.3924 kW, but for some reason the equipmentsummary report is computing 271.998.79 kW(more details blow).

Given Data:
Name	MAU-1 AHU Cooling Coil
Availability Schedule Name	2
Design Water Flow Rate	0.015170
Design Air Flow Rate	16.239000
Design Inlet Water Temperature	7.22
Design Inlet Air Temperature	34.06
Design Outlet Air Temperature	22.92
Design Inlet Air Humidity Ratio	0.021
Design Outlet Air Humidity Ratio	0.016
Water Inlet Node Name	MAU-1 AHU Cooling Coil Water Inlet Node
Water Outlet Node Name	MAU-1 AHU Cooling Coil Water Outlet Node
Air Inlet Node Name	MAU-1 AHU Mixed Air Outlet
Air Outlet Node Name	MAU-1 AHU Cooling Coil Air Outlet Node
Type of Analysis	SimpleAnalysis
Heat Exchanger Configuration	CrossFlow
Condensate Collection Water Storage Tank Name	


REPORT:	EquipmentSummary

Cooling Coils

	MAU-1 AHU COOLING COIL
Type	Coil:Cooling:Water
Nominal Total Capacity [W]	271998.79
Nominal Sensible Capacity [W]	197754.52
Nominal Latent Capacity [W]	74244.27
Nominal Sensible Heat Ratio	0.73
Nominal Efficiency [W/W]	-
Nominal Coil UA Value [W/C]	18545.91
Nominal Coil Surface Area [m2]	188.1





------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/