[EnergyPlus_Support] VAV minimum flow setpoints



Hello all,
I am trying to set the minimum air flow of the VAV boxes to satisfy the 
G3.1.3.13 requirement, which says that "Minimum volume setpoints for VAV 
reheat boxes shall be 2.15 L/s.m2 of floor area served or the minimum 
ventilation rate, whichever is larger".

The zone area is 518.49 m2 and the ventilation rate is 0.733 m3/s. So 
the minimum flow rate that I should use according to G3.1.3.13 is 518.49 
* 2.15 / 1000 = 1.115 m3/s, since it is larger than 0.733 m3/s.

This is how I've put it in EnergyPlus:

  AirTerminal:SingleDuct:VAV:Reheat,
     F002 VAV Reheat,         !- Name
     Always On,               !- Availability Schedule Name
     F002 Damper Outlet,      !- Damper Air Outlet Node Name
     F002 Zone Equip Inlet,   !- Air Inlet Node Name
     autosize,                !- Maximum Air Flow Rate {m3/s}
     FixedFlowRate,           !- Zone Minimum Air Flow Input Method
     ,                        !- Constant Minimum Air Flow Fraction
     1.115,                   !- Fixed Minimum Air Flow Rate {m3/s}
     ,                        !- Minimum Air Flow Fraction Schedule Name
     Coil:Heating:Water,      !- Reheat Coil Object Type
     F002 Reheat Coil,        !- Reheat Coil Name
     autosize,                !- Maximum Hot Water or Steam Flow Rate 
{m3/s}
     0,                       !- Minimum Hot Water or Steam Flow Rate 
{m3/s}
     F002 Supply Inlet,       !- Air Outlet Node Name
     0.001,                   !- Convergence Tolerance
     Reverse;                 !- Damper Heating Action

The output results for F002 Zone Equip Inlet (System Node Volume Flow 
Rate Standard Density) show 0.733 m3/s.

What am I doing wrong and how to set the minimum flow setpoints 
according to G3.1.3.13 correctly?

Thank you!
Miroslav




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/