Fan Pressure should have zero bearing on unmet loads. Its only function is to calculate electricity consumption. even though the motor heat will enter the airstream if it is designated as being in the airstream, I doubt this is your problem. That being said, your method for baseline fan power sizing by adjustment of the pressure rise looks right. You are allowed 300 hours unmet load, as long as the design case also has 250 or more but less than 300 (deviation of 50), though proper setpoint management should keep you under 50 for a good model. Sent from my iPhone
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.