Hi,
I'm getting the following warning for all the zones while trying to model a building located in climate zone 1.
** Warning ** Calculated design cooling load for zone=OS:THERMALZONE 7 is zero.
** ~~~ ** Check Sizing:Zone and ZoneControl:Thermostat inputs.
** Warning ** Calculated design heating load for zone=OS:THERMALZONE 7 is zero.
** ~~~ ** Check
Sizing:Zone and ZoneControl:Thermostat inputs.
I've used the following single heating and single cooling setpoint schedule using SizingPeriod:WeatherFileConditionType.
Schedule:Compact,
Htg-SetP-Sch, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: WinterTypical, !- Field 2
Until: 24:00, !- Field 3
21; !- Field 4
For: SummerTypical, !- Field 5
Until: 24:00, !- Field 6
11; !- Field 7
For: AllOtherDays, !- Field 8
Until:
24:00, !- Field 9
21; !- Field 10
Schedule:Compact,
Clg-SetP-Sch, !- Name
Temperature, !- Schedule Type Limits Name
Through: 12/31, !- Field 1
For: SummerTypical, !- Field
2
Until: 24:00, !- Field 3
23; !- Field 4
For: WinterTypical, !- Field 5
Until: 24:00, !- Field 6
50; !- Field 7
For: AllOtherDays,
!- Field 8
Until: 24:00, !- Field 9
23; !- Field 10
I have used ZoneInfiltration:DesignFlowRate for the infiltration of 1.024 l/s/m2 using flow/exteriorarea as the design flow rate calculation method. I have also checked the internal gain inputs and they don't seem to be too high or low. The lighting power is in line with ASHRAE 90.1 requirements, number of people is 0.04 person/m2 and equipment load is 2.7
W/m2.
Any suggestions?
Thanks,
Aber