Re: [EnergyPlus_Support] VAV cooling still working when room T is lower than setpoint T
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: Re: [EnergyPlus_Support] VAV cooling still working when room T is lower than setpoint T
- From: Richard Raustad <RRaustad@xxxxxxxxxxxx>
- Date: Fri, 08 Feb 2013 12:21:54 -0500
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Fri, 08 Feb 2013 10:21:57 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1360344116; bh=Rhi2GNQtKvr/vVg3hqBVUkdRE+o+Z8a0eO4UlE2v068=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:In-reply-to:To:Message-id:Organization:User-Agent:References:X-Originating-IP:X-eGroups-Msg-Info:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=xXg5cjD6+QaqWRHM7kZeCUHLm4Qw8hiY9Nhn92lpkB19zceLfMr3L8dvDEDmDfX8nF8cjQiO45cLAVSv5G0YfuRlZwY7KZDPIjW3xB5rk3oAHlUqgBhyqJFQtaZwgbdiL+TzdeYGrxK1zxKEQFLKN3GfQd2KFEKPLWYQVPUogU0=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=RP5bagGxeUY3UrFwaJkhM/yq7dwotR7JENtkIl7KifRjMgg3ITaQ63iXhQis9MJe9pJlDc2w70fmGY3uBpYTrHiSXAD5WPYaiAcJ4ZJKt03y8R8slKpXP0fJt9rEgpAsZByXQLrkobdhw+cBvlDAqyuQya1xSTdLjSgkQwbodRQ=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <51153291.3050307@yahoo.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Organization: Florida Solar Energy Center
- References: <51153291.3050307@yahoo.com>
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: Mozilla/5.0 (Windows NT 5.1; rv:17.0) Gecko/20130107 Thunderbird/17.0.2
Find out which water cooling coil is requesting flow. Any flow request
on the demand side of the loop with turn on the plant.
Report coil water inlet node volume flow rate for all water cooling coils.
This should tell you which cooling coil is operating. Then determine why
this one (or more) coil(s) is operating.
It may be that the VAV cooling coil is trying to meet a low set point
temperature even though the room thermostats are satisfied.
On 2/8/2013 12:14 PM, HJ wrote:
> Hi all,
>
> I notice the VAV system is still running even if room T is way below
> setpoint T (e.g. at night ,Tsetpoint is 26, Troom is 22 something).
> However, CAV system does not have this type of problem. Since I am
> modeling hybrid ventilation, I would like the VAV system shut down when
> Troom meets Tset. Is there a way to achieve that?
>
> Thanks,
>
> HJ
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:
> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo! Groups Links
>
>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 40 Years
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/