[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Heat gain through wall_Output Variable





Thank you. When i try to use following variable the heat gain has negative value. Any thoughts?

Output:Variable,*,Surface Inside Face Convection Heat Gain Rate,hourly; !- Zone Average [W]

On Fri, Feb 8, 2013 at 2:02 PM, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 

Javed,

 

Here are some examples:

Output:Variable,*,Surface Inside Face Convection Heat Transfer Coefficient,hourly; !- Zone Average [W/m2-K]

Output:Variable,*,Surface Inside Face Convection Heat Gain Rate,hourly; !- Zone Average [W]

Output:Variable,*,Surface Inside Face Convection Heat Gain Rate per Area,hourly; !- Zone Average [W/m2]

Output:Variable,*,Surface Inside Face Convection Heat Gain Energy,hourly; !- Zone Sum [J]

Output:Variable,*,Surface Inside Face Net Surface Thermal Radiation Heat Gain Rate,hourly; !- Zone Average [W]

Output:Variable,*,Surface Inside Face Net Surface Thermal Radiation Heat Gain Rate per Area,hourly; !- Zone Average [W/m2]

Output:Variable,*,Surface Inside Face Net Surface Thermal Radiation Heat Gain Energy,hourly; !- Zone Sum [J]

Output:Variable,*,Surface Inside Face Solar Radiation Heat Gain Rate,hourly; !- Zone Average [W]

Output:Variable,*,Surface Inside Face Solar Radiation Heat Gain Rate per Area,hourly; !- Zone Average [W/m2]

 

Note that you should specify in your IDF:

Output:VariableDictionary,IDF;

This will create a .rdd file which contains a listing of all possible report variables.  There are literally hundreds (or more).  I have only shown a few samples ? there are more that might work better for you.

 

 

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Javed Iqbal
Sent: Friday, February 08, 2013 1:54 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Heat gain through wall_Output Variable

 

 

Hi,

 

I'm trying to get total heat gain through external wall in a zone. I found following variable gives surface heat gain.

 

Surface Inside Face Net Surface Thermal Radiation Heat Gain Rate 

Surface Outside Face Solar Radiation Heat Gain Rate  

 

Can anybody suggest me what output variable i need to choose for this??

 

Thanks,

--

 

 

Javed Iqbal, LEED AP, CEA

Energy Analyst 

 

 

 

 

 




--


Javed Iqbal, LEED AP, CEA
Energy Analyst 







__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___