[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: COP of AirLoopHVAC:UnitaryHeatPump:AirToAir
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: COP of AirLoopHVAC:UnitaryHeatPump:AirToAir
- From: "FrancescoP" <direzionecontraria@xxxxxxxx>
- Date: Fri, 15 Feb 2013 09:20:02 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Fri, 15 Feb 2013 02:20:05 -0700
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1360920004; bh=LZ+ohiVqXlm3ET4m1lnhawwyHbJFDBKKOJIEhCvz8Mk=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=VleQ1HmU5CsDuULZagR7uXYs3Gvi9tbJcs/7GxEYcK9OZBjs97S221UCQy8gAfoTPJzV1p5bZHWou6Rrh0pBr9UzONTVlLVQ0ELDC3qH10jtzxpODmeRslRE6cukUPLuaVSMmuh+M0u6AFOCZipGmtFY9WPIMnkTMlPMC4rLp/E=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=I3snAkdRuRIUCG1bobDDgg+lqfEZ/pYV19dNtbTgPurvdUN+lHn90Sv1HhUVPSGdrt81Yuwz2VtWBOWpKJzJwi96j9MJ79odqFb9YeZdmtdKDKvlfDTZNfp9/phdVDsAgA/qr0UGyV7QLf7L13bpDS7VvU5Q15Pve7YdCWBygqM=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <511D35CE.6000902@fsec.ucf.edu>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
"The EIR is the inverse of the COP."
Sorry. I misunderstood.
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad wrote:
>
> You defined COP in your email. How would you define EIR?
>
> Using constant curves for the baseline sounds like cheating to me.
>
>
> On 2/14/2013 9:35 AM, FrancescoP wrote:
> > Thank you, Mr. Raustad.
> > You are right: the function proposed by DesignBuilder is valid only for x values (i.e. indoor coil entering air temperature) between 12.77 and 23.88°C. I was wrong because I plotted the graph for indoor coil entering air temperature equal to 31°C. Now I have plotted the graph for indoor coil entering air temperature equal to 23°C:
> > http://imageshack.us/f/844/db23.jpg/
> > Yes, I divided heating capacity factor by EIR (energy input factor). I think that the result is the factor that multiplies the COP, isn't it? I don't understand why you wrote the "The COP is 1/EIR" (energy input factor). COP is defined as "the ratio of the rate of heat delivered to the rate of energy input".
> > I have plotted also come curves from RooftopPackagedHeatPump.idf
> > http://imageshack.us/f/716/jcip.jpg/
> > Yes, there are examples where both heating capacity and power increase as outdoor temps increase but capacity increases faster than power leading to an increasing COP:
> > http://www.rheem.co.nz/UserFiles/1/image/commercial-heat-pump-cop-vs-temp.jpg
> > Actually, I'm wondering whether for a baseline model for LEED certification I could use constant curves. It would be unrealistic but the baseline model has not to correspond to a real situation.
> > With Regards
> > Francesco Passerini
> >
> >
> > --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad wrote:
> >> What is the range (min/max) on the x (indoor coil entering air temp) and
> >> y (outdoor coil entering air temp) curve inputs if used? These limits
> >> can influence the results (the curves output, which also has limits if
> >> used). Also, 31C is rather high for the indoor coil entering air temp.
> >> How does this look for other lower temps. You should plot at least 2
> >> indoor coil entering air temps on the chart to ensure the curves act
> >> accordingly.
> >>
> >> It looks like you divided heating capacity factor by EIR (energy input
> >> factor). The COP is 1/EIR which would show an increase in COP as outdoor
> >> temp increased.
> >>
> >> I see a downward trend in heating capacity as outdoor air temp increases
> >> at higher outdoor temps. Find some manufacturers data and verify this is
> >> correct (or look in the data sets file RooftopPackagedHeatPump.idf).
> >> This curve appears incorrect to me (i.e., capacity should increase as
> >> outdoor air temp increases). Heating capacity and power should both
> >> increase as outdoor temps increase. But capacity increases faster than
> >> power leading to an increasing EER and COP.
> >>
> >> Always question the performance curves since these are what is actually
> >> simulated.
> >>
> >>
> >> On 2/13/2013 6:35 AM, FrancescoP wrote:
> >>> I used curves that are used as default in DesignBuilder: DXClgCoilTotalClgCapFuncTemperature and DXClgCoilEnergyInputRatioFuncTemperature
> >>> They are Curve:Biquadratic
> >>> I have plotted them (hopefully correctly)considering the condenser temperature 31°C:
> >>> http://imageshack.us/f/580/dbcurves.jpg/
> >>> It is a "baseline model" therefore it doesn't correspond to a real HVAC system.
> >>> I have seen that in some examples of EnergyPlus as curves for "Total Heating Capacity Function of Temperature Curve" and for "Energy Input Ratio Function of Temperature Curve" objects Curve:Cubic are used (see AirflowNetwork_MultiZone_House.idf in that case if external temperature increases COP increases). Do you think that neglecting the influence of the condenser temperature on the COP is an acceptable approximation?
> >>> I simulated using those curves. Here the graph with the curves proposed by AirflowNetwork_MultiZone_House.idf :
> >>> http://imageshack.us/f/560/copu.jpg/
> >>> (comparing with the previous graph consider that in the meantime also the peak power of the heat pump was changed)
> >>> Probably I will develop curves using Curve:Biquadratic in order to consider both the condenser temperature and the evaporator temperature. I have found some interesting graphs in H. Ludwig von Cube et al. (1981) "Heat pump technology", Butterworths and in (1979) "Heat pump technology for saving energy", Noyes data corporation.
> >>>
> >>>
> >>>
> >>> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "FrancescoP" wrote:
> >>>> I am modeling System 4 - PSZ-HP according to the definition of Annex G of ASHRAE 90.1-2007. In excel I calculated the COP as ratio between "DX Coil Total Heating Rate" and "DX Heating Coil Electric Power" and I plotted the graph (outdoor air temperature ; COP) that you can see here:
> >>>> http://imageshack.us/f/442/copg.jpg/
> >>>> (when the "DX Heating Coil Electric Power" is equal to 0 I imposed the COP equal to 0)
> >>>> In the object AirLoopHVAC:UnitaryHeatPump:AirToAir the field "Maximum Outdoor Dry-Bulb Temperature for Supplemental Heater Operation" is equal to 4°C. I think that is the reason why the COP decreases between 3°C and 5°C: the electric heating coil switches off and the DX coil has to heat the supply air to a greater temperature.
> >>>> The COP decreases also when the outside temperatures are greater than 10°C. I don't understand why.
> >>>> Any comment, please?
> >>>> Best Regards
> >>>> Francesco Passerini
> >>>>
> >>>
> >>> ------------------------------------
> >>>
> >>> Primary EnergyPlus support is found at:
> >>> http://energyplus.helpserve.com or send a message to energyplus-support@
> >>>
> >>> The primary EnergyPlus web site is found at:
> >>> http://www.energyplus.gov
> >>>
> >>> The group web site is:
> >>> http://groups.yahoo.com/group/EnergyPlus_Support/
> >>>
> >>> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
> >>>
> >>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> >>> Yahoo! Groups Links
> >>>
> >>>
> >>>
> >>>
> >> --
> >> Richard A. Raustad
> >> Senior Research Engineer
> >> Florida Solar Energy Center
> >> University of Central Florida
> >> 1679 Clearlake Road
> >> Cocoa, FL 32922-5703
> >> Phone: (321) 638-1454
> >> Fax: (321) 638-1439 or 1010
> >> Visit our web site at: http://www.fsec.ucf.edu
> >>
> >> UCF - From Promise to Prominence: Celebrating 40 Years
> >>
> >
> >
> >
> > ------------------------------------
> >
> > Primary EnergyPlus support is found at:
> > http://energyplus.helpserve.com or send a message to energyplus-support@...
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> > Yahoo! Groups Links
> >
> >
> >
> >
>
> --
> Richard A. Raustad
> Senior Research Engineer
> Florida Solar Energy Center
> University of Central Florida
> 1679 Clearlake Road
> Cocoa, FL 32922-5703
> Phone: (321) 638-1454
> Fax: (321) 638-1439 or 1010
> Visit our web site at: http://www.fsec.ucf.edu
>
> UCF - From Promise to Prominence: Celebrating 40 Years
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/