Hello Pankaj, To keep the same sizing data for different runs, you have to set all the fields with the key-world â??autosizeâ?? to the value calculated in your first run.
HVACTemplate:System:VAV, VAV with Reheat, !- Name Office HVAC, !- System Availability Schedule Name autosize, !- Supply Fan Maximum Flow Rate {m3/s} autosize, !- Supply Fan Minimum Flow Rate {m3/s} 0.7, !- Supply Fan Total Efficiency 1000, !- Supply Fan Delta Pressure {Pa} 0.9, !- Supply Fan Motor Efficiency 1, !- Supply Fan Motor in Air Stream Fraction ChilledWater, !- Cooling Coil Type , !- Cooling Coil Availability Schedule Name , !- Cooling Coil Setpoint Schedule Name 13, !- Cooling Coil Design Setpoint {C} None, !- Heating Coil Type , !- Heating Coil Availability Schedule Name , !- Heating Coil Setpoint Schedule Name 10.0, !- Heating Coil Design Setpoint {C} 0.8, !- Gas Heating Coil Efficiency , !- Gas Heating Coil Parasitic Electric Load {W} None, !- Preheat Coil Type , !- Preheat Coil Availability Schedule Name , !- Preheat Coil Setpoint Schedule Name 7.2, !- Preheat Coil Design Setpoint {C} 0.8, !- Gas Preheat Coil Efficiency , !- Gas Preheat Coil Parasitic Electric Load {W} autosize, !- Maximum Outdoor Air Flow Rate {m3/s} autosize, !- Minimum Outdoor Air Flow Rate {m3/s} ProportionalMinimum, !- Minimum Outdoor Air Control Type Office Minimum OA, !- Minimum Outdoor Air Schedule Name FixedDryBulb, !- Economizer Type NoLockout, !- Economizer Lockout , !- Economizer Upper Temperature Limit {C} , !- Economizer Lower Temperature Limit {C} , !- Economizer Upper Enthalpy Limit {J/kg} , !- Economizer Maximum Limit Dewpoint Temperature {C} , !- Supply Plenum Name PLENUM, !- Return Plenum Name DrawThrough, !- Supply Fan Placement InletVaneDampers, !- Supply Fan Part-Load Power Coefficients StayOff, !- Night Cycle Control , !- Night Cycle Control Zone Name None, !- Heat Recovery Type 0.7, !- Sensible Heat Recovery Effectiveness 0.65, !- Latent Heat Recovery Effectiveness None, !- Cooling Coil Setpoint Reset Type None, !- Heating Coil Setpoint Reset Type , !- Dehumidification Control Type , !- Dehumidification Control Zone Name , !- Dehumidification Setpoint {percent} , !- Humidifier Type , !- Humidifier Availability Schedule Name , !- Humidifier Rated Capacity {m3/s} , !- Humidifier Rated Electric Power {W} , !- Humidifier Control Zone Name , !- Humidifier Setpoint {percent} NonCoincident; !- Sizing Option
Florian
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Pankaj Chawla <pankaj013@...> wrote: > > Hi > > Am pretty new to EPlus so not sure if the answer is straight forward but couldn't find it in the documentation so here it is: > > I ran a simulation of a sample building (Tutorial 2B as per Getting Started Document) with no weather data in sizing mode. > The simulation returns some plant and air flow sizing data back. What I want to do next is force my subsequent simulations > to use the sizing data from simulation 1 and rerun simulations with different weather files to see what the response of the > same system would be if installed in different climate zones. Is there a way to configure EPlus to use equipment sizing > data arrived for a particular simulation run to be used for all subsequent runs? > > --- > Take care, > Pankaj >