Re: [EnergyPlus_Support] Radiant and Operative temperature





Use AirIdealLoads. It will input energy to control the zone temp to whatever you set it and is the least you can do to control zone temperature. You can even use a comfort thermostat object to control based upon comfort levels - awesome tool to explore the built environment and how it'll feel in your building.

ZoneHVAC:IdealLoadsAirSystem,
Zone1 Ideal Loads System, !- Name
AlwaysOn, !- Availability Schedule Name
Zone1 Ideal Loads Supply Node, !- Zone Supply Air Node Name
Zone1 Ideal Loads Return Node, ! Zone Exhaust Air Node Name
50, !- Maximum Heating Supply Air Temperature {C}
13, !- Minimum Cooling Supply Air Temperature {C}
0.0156, !- Maximum Heating Supply Air Humidity Ratio {kg-H2O/kg-air}
0.0077, !- Minimum Cooling Supply Air Humidity Ratio {kg-H2O/kg-air}
NoLimit, !- Heating Limit
, !- Maximum Heating Air Flow Rate {m3/s}
, !- Maximum Sensible Heating Capacity {W}
NoLimit, !- Cooling Limit
, !- Maximum Cooling Air Flow Rate {m3/s}
, !- Maximum Total Cooling Capacity {W}
, !- Heating Availability Schedule Name
, !- Cooling Availability Schedule Name
None, !- Dehumidification Control Type
0.7, !- Cooling Sensible Heat Ratio
None, !- Humidification Control Type
Office OA Specification, !- Design Specification Outdoor Air Object Name
Zone1 Ideal Loads OA Inlet Node, !- Outdoor Air Inlet Node Name
None, !- Demand Controlled Ventilation Type
NoEconomizer, !- Outdoor Air Economizer Type
None, !- Heat Recovery Type
0.70, !- Sensible Heat Recovery Effectiveness
0.65; !- Latent Heat Recovery Effectiveness

Jason Quinn
+64 21 1846 911


On Sat, Apr 6, 2013 at 3:06 AM, yiolari87 <georgiou.geo13@xxxxxxxxx> wrote:
 

Hello group,

I want to estimate the mean radiant temperature and operative temperature of a zone, in a building. However, I was thinking that instate of simulating the whole building and its zone, to set the air temperature of the zone and in conjunction with the external environment to estimate the indoor variables that I need.

Does anybody know how to set the air temperature of a zone without employing any HVAC system?

Thank you in advance
George Georgiou




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___