|
How do you expect the program to calculate air flow from one side of a single zone to another side of a single zone through an "internal door"? The zone by definition is only one air node. You need to create multiple zones. E+ will accept zone internal constructions and they will contribute to the internal mass, surface-surface radiation exchange and surface-zoneair convection exchange...but be very careful how infalling solar radiation is handled and what calculation model you are using (FullInteriorAndExteriorwithReflections?). Hope this gives some insight, Regards, Jean Sent from my iPhone
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |