i have the same problem with energy modeling in some buildings that pursue the LEED certification.
my aproach to the problem after some projects and many observations by the LEED review team using energyplus as modeling software is:
1. using the equations showed in ASHRAE 90.1 users guide G-A, G-B and G-C help me to direct the conversion of EER at ARI condition exposed in ASHRAE 90.1 to nominal efficiency that is the data required to define in energyplus.
2. using a preliminar simulation in energyplus with a any efficiency (EER 2.7 by example), the Gross Cooling Capacity and Net Cooling Capacity recorded in the Equipment Summary are used to estimate the Suply Fan Power at ARI conditions (based on equations G-A and G-C):
G-A = EER [rated 90.1] = Net Cooling Cap [W] / Total Power Input[W] = (Gross Cooling Capacity [W] - Supply Fan Power [W]) / Total Power Input [W]
3 using these results i can calculate the supply fan power at rated conditions
Supply Fan Power [W] = Nominal Total Cap [W] - Std. Rating (net) Cooling Capacity [W]
Total Power Input [W] = Net Cooling Capacity [W] / EER at rated conditions of 90.1 [SI]
4 to calculate the final nominal efficiency for use in energyplus simulation:
Nominal Efficiency [Energyplus] = Gross Cooling Capacity [W] / (Total Power Input[W] - Supply Fan Power[W])
tip:
i review the equipment summary from energyplus final simulation and compare the EER at ARI condition (not nominal EER used as input) with ASHRAE 90.1 to confirm that the procedure is correct.
I hope the information wil be helpful.