James, thanks!
this will be a great help! good job to all!
Téc. Ivan Mezzacapa Desenhista Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Celular: (11)9963-9326To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx Date: Tue, 16 Apr 2013 19:48:11 -0500 Subject: RE: [EnergyPlus_Support] Baseline Pressure Rise Formatting was terrible below. Try this:
James V Dirkes II, PE, BEMP, LEED AP
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jim Dirkes
Ivan, The derivation below is in IP units, but it should give you some guidance. As an example, pressure rise of 1.28 inches w.c. or 318 Pascals produces correct fan power for Sytems 1 or 2. For System 3 or 4, itâ??s 3.32 inches w.c. or 826 Pa (No pressure credit) For Systems 5 â?? 8, 4.59 in. w.c. or 1142 Pa (No pressure credit)
James V Dirkes II, PE, BEMP, LEED AP
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Ivan Mezzacapa
Hi!
how can i calculate pressure rise for baseline model?
Thanks! Téc. Ivan Mezzacapa Desenhista Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Celular: (11)9963-9326 __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.