[EnergyPlus_Support] Re: Air volume flow rate - related warning message
I'm getting the same warnings. I'm using a Fan:VariableVolume in combination with a Coil:CoolingDX:SingleSpeed
It is a baseline model according to ASHRAE 90.1-2007 (system 6).
Do you think that replacing the Coil:CoolingDX:SingleSpeed with a Coil:Cooling:DX:TwoStageWithHumidityControlModee would be the solution?
Regards
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "Michael J. Witte" <mjwitte@...> wrote:
>
> Sorry this was not answered sooner.
>
> Without seeing the input file, it is difficult to guess. Is everything in the
> system autosized? If there is a mix of hard values for some flow rates and
> autosized values for others, the autosizing routines know nothing of the hard
> values entered in individual component objects. They only know of hard flow
> rates entered in ZONE SIZING and SYSTEM SIZING objects.
>
> How serious? That is hard to say. In this case, the flow rate is only
> slightly out of range. But in general, DX equipment is typically designed to
> operate well inside this range of flows/capacity. So, if the warnings trip, it
> usually means something is not entered correctly.
>
> Mike
>
>
>
>
> On 21 Aug 2007 at 14:19, krgowri wrote:
>
> > I am looking for help to understand and resolve this warning message.
> > In this case, both the capacity and flow rates are autosized.
> >
> > How is the air flow rate range determined? The warning suggests I use
> > a different coil type. Has anyone experimented with changing the coil
> > type? How serious is this warning in terms of the simulation results?
> >
> > ** Warning ** COIL:DX:COOLINGBYPASSFACTOREMPIRICAL "SYS1 DX COOLING
> > COIL" - Air volume flow rate per watt of rated total cooling capacity
> > is out of range at 6.717909491932784E-005 m3/s/W.
> > ** ~~~ ** Occurrence info=ANCHORAGE AK USA TMY2-26451
> > WMO#=702730, 11/10 11:00 - 11:04
> > ** ~~~ ** Expected range for VolumeFlowperRatedTotalCapacity=[
> > 2.684000000000000E-005-- 6.713000000000000E-005]
> > ** ~~~ ** Possible causes include inconsistent air flow rates
> > in system components,
> > ** ~~~ ** or variable air volume [VAV] system using incorrect
> > coil type.
> >
> >
> >
> >
> > The primary EnergyPlus web site is found at:
> > http://www.energyplus.gov
> >
> > The group web site is:
> > http://groups.yahoo.com/group/EnergyPlus_Support/
> >
> > Attachments are not allowed -- please post any files to the appropriate folder
> > in the Files area of the Support Web Site.
> >
> > EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the
> > Documentation link and press the "search" button.
> >
> > Yahoo! Groups Links
> >
> >
> >
> >
> >
>
>
> ========================================================
> Michael J. Witte, GARD Analytics, Inc.
> EnergyPlus Testing and Support
> EnergyPlus-Support@...
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://docs.yahoo.com/info/terms/