My most recent analysis was an unconditioned building with lots of solar gain. I tried iterating slab with calculated space temperatures, but it would not
match my measured conditions during the summer. I could only match measured summer conditions by manually inputting under slab temperature values. I think a hint about the issue is that slab works with the space temperature but does not concern itself with
solar gain. Slab probably works fine for a dark basement. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of FrancescoP I add that I'm considering F. Droulia et al (2009) "Ground temperature estimations using simplified analytical and semi-empirical approaches" and other methods in order to estimate the ground temperature to use in the object
Site:GroundTemperature:BuildingSurface __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.