|
I have a little urgency with this problem and can not figure out. If anyone knows anything, any comments greatly help. Thank you all! Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326To: energyplus_support@xxxxxxxxxxxxxxx From: ivan_slip@xxxxxxxxxxx Date: Tue, 11 Jun 2013 17:25:50 +0000 Subject: [EnergyPlus_Support] Heating Load = Zero? Hi! i need a help. My simulation is giving this error however, I pointed out all the capabilities and equipment in their respective environments. My thermostats are normal. These are the errors: ** Warning ** Calculated design cooling load for zone = bloco7: SALA15 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco7: SALA15 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design cooling load for zone = bloco7: SALA14 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco7: SALA14 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design cooling load for zone = bloco7: SALA13 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco7: SALA13 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design cooling load for zone = bloco6: SALA04 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. ** Warning ** Calculated design heating load for zone = bloco6: SALA04 is zero. ~ ** ~ ~ ** Check Sizing: Zone and ZoneControl: Thermostat inputs. This is happening in all environments and not know why. Thank you! Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor de Eficiência Energética em Ar Condicionado LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |