Is the supply air flow rate into that zone at the maximum?
On 6/12/2013 4:15 PM, FCoelho wrote:
> NO multiplier.
>
>
> --- In EnergyPlus_Support@xxxxxxxxxxxxxxx, Richard Raustad <RRaustad@...> wrote:
>> Does that zone have a multiplier?
>>
>> On 6/12/2013 2:21 PM, FCoelho wrote:
>>> Dear All,
>>>
>>> I believe this should have a simple answer, still I didn't got there yet.
>>>
>>> I'm reporting on :
>>> ZoneX :Zone Mechanical Ventilation Air Change Rate [ach](TimeStep)
>>> ZoneX : :People Number Of Occupants [](TimeStep)
>>>
>>> I have the outdoor air defined as Flow/Person at 0.01 m³ in the DesignSpecification outdoor air, and I'm using the ideal loads Air system referring to this.
>>>
>>> At a particular timestep I have 2.14 ACH which gives me around 0.205 m³/s (ZoneVolume=343.8091 m³) with 26.86 occupants. However I was expecting 0.01 m³/s * 26.86 occ. = 2.6 m³/s.
>>>
>>> What am I missing?
>>> Thank you all for any help provided.
>>>
>>>
>>>
>>>
>>> ------------------------------------
>>>
>>> Primary EnergyPlus support is found at:
>>> http://energyplus.helpserve.com or send a message to energyplus-support@...
>>>
>>> The primary EnergyPlus web site is found at:
>>> http://www.energyplus.gov
>>>
>>> The group web site is:
>>> http://groups.yahoo.com/group/EnergyPlus_Support/
>>>
>>> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>>>
>>> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
>>> Yahoo! Groups Links
>>>
>>>
>>>
>>>
>> --
>> Richard A. Raustad
>> Senior Research Engineer
>> Florida Solar Energy Center
>> University of Central Florida
>> 1679 Clearlake Road
>> Cocoa, FL 32922-5703
>> Phone: (321) 638-1454
>> Fax: (321) 638-1439 or 1010
>> Visit our web site at: http://www.fsec.ucf.edu
>>
>> UCF - From Promise to Prominence: Celebrating 50 Years
>>
>
>
>
> ------------------------------------
>
> Primary EnergyPlus support is found at:> http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
>
> The primary EnergyPlus web site is found at:
> http://www.energyplus.gov
>
> The group web site is:
> http://groups.yahoo.com/group/EnergyPlus_Support/
>
> Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
>
> EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.> Yahoo! Groups Links
>
>
>
>
--
Richard A. Raustad
Senior Research Engineer
Florida Solar Energy Center
University of Central Florida
1679 Clearlake Road
Cocoa, FL 32922-5703
Phone: (321) 638-1454
Fax: (321) 638-1439 or 1010
Visit our web site at: http://www.fsec.ucf.edu
UCF - From Promise to Prominence: Celebrating 50 Years
__._,_.___