How about splitting the zone into 2 zones seperated with an IRTransparent wall. I believe the energy transfered by the IRTransparent wall is treated the same as diffuse radiation...or?

Remember to set the convection coeff. to very small so that it does not participate in convection to the zone.

Material:InfraredTransparent,
IRTMaterial1; !- Name
Construction,
IRTSurface, !- Name
IRTMaterial1; !- Outside Layer
SurfaceProperty:ConvectionCoefficients,
Bottom:Top, !- SurfaceName
Outside, !- Convection Type 1
value, !- Convection Value Type 1
0.1, !- Convection value 1 {W/m2-K}
, !- Convection Schedule 1
Inside, !- Convection Type 2
value, !- Convection Value Type 2
0.1; !- Convection value 2 {W/m2-K}
SurfaceProperty:ConvectionCoefficients,
SecondLevel:Bottom, !- SurfaceName
Outside, !- Convection Type 1
value, !- Convection Value Type 1
0.1, !- Convection value 1 {W/m2-K}
, !- Convection Schedule 1
Inside, !- Convection Type 2
value, !- Convection Value Type 2
0.1; !- Convection value 2 {W/m2-K}
SurfaceProperty:ConvectionCoefficients,
SecondLevel:Top, !- SurfaceName
Outside, !- Convection Type 1
value, !- Convection Value Type 1
0.1, !- Convection value 1 {W/m2-K}
, !- Convection Schedule 1
Inside, !- Convection Type 2
value, !- Convection Value Type 2
0.1; !- Convection value 2 {W/m2-K}
SurfaceProperty:ConvectionCoefficients,
ThirdLevel:Bottom, !- SurfaceName
Outside, !- Convection Type 1
value, !- Convection Value Type 1
0.1, !- Convection value 1 {W/m2-K}
, !- Convection Schedule 1
Inside, !- Convection Type 2
value, !- Convection Value Type 2
0.1; !- Convection value 2 {W/m2-K}



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/