[EnergyPlus_Support] Baseboard:Convective:Electric: results varies with detailed / global equipements



Hi all,

I am modelling a building with an energy recovery ventilator, an exchanger with an efficiency of 80% and electric baseboards which provides the missing energy. To avoid creating the entire airflow network, I have entered one ERV per zone.

I want to know what is the consumption of the baseboard, and so at first I modelled one electric baseboard linked with all of the ERV. The results were quite low, 880 kWh for 305 m² the whole year.

Then I wanted to know what was the consumption for each zone of the building and I created separated baseboards for each zone and connected them to corresponding ERV. The results were then much higher, 14300 kWh for 305 m².

I can't figure out why there is such a difference between the two simulations, the setpoint in every room is always met, any ideas ?

Below is the corresponding part of the .idf

Antoine





!-   ===========  ALL OBJECTS IN CLASS: ZONECONTROL:THERMOSTAT ===========

ZoneControl:Thermostat,
    Thermostat_N401,         !- Name
    T2 Chambre,              !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N402,         !- Name
    T2_Salon_Ouest,          !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N403,         !- Name
    T3 Nord Sejour,          !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N404,         !- Name
    T3 Nord Chambre 1,       !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N405,         !- Name
    T3 Nord Chambre 2,       !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N406,         !- Name
    T3 Sud Salon,            !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N407,         !- Name
    T3 Sud Chambre 1,        !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N408,         !- Name
    T3 Sud Chambre 2,        !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N409,         !- Name
    T4 Chambre 3,            !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N410,         !- Name
    T4 Salon,                !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N411,         !- Name
    T4 Chambre 1,            !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N412,         !- Name
    T4 Chambre 2,            !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N413,         !- Name
    T2 SdB,                  !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dualsdb;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N414,         !- Name
    T3 Nord SdB,             !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dualsdb;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N415,         !- Name
    T3 Nord Cuisine,         !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N416,         !- Name
    T3 Sud Cuisine,          !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N417,         !- Name
    T3 Sud SdB,              !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dualsdb;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N418,         !- Name
    T4 SdB,                  !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dualsdb;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N419,         !- Name
    T4 Cuisine,              !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N420,         !- Name
    T3 Nord Couloir,         !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N421,         !- Name
    T3 Sud Couloir,          !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name

ZoneControl:Thermostat,
    Thermostat_N422,         !- Name
    T4 Couloir,              !- Zone or ZoneList Name
    Zone Control Type Sched, !- Control Type Schedule Name
    ThermostatSetpoint:DualSetpoint,  !- Control 1 Object Type
    dual N4;                 !- Control 1 Name


!-   ===========  ALL OBJECTS IN CLASS: THERMOSTATSETPOINT:DUALSETPOINT ===========

ThermostatSetpoint:DualSetpoint,
    dual N4,                 !- Name
    Heating N4,              !- Heating Setpoint Temperature Schedule Name
    Cooling Setpoints;       !- Cooling Setpoint Temperature Schedule Name

ThermostatSetpoint:DualSetpoint,
    dualsdb,                 !- Name
    Heating sdb,             !- Heating Setpoint Temperature Schedule Name
    Cooling Setpoints;       !- Cooling Setpoint Temperature Schedule Name


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:ENERGYRECOVERYVENTILATOR ===========

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT2_chambre,           !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-01,         !- Heat Exchanger Name
    0.0055,                  !- Supply Air Flow Rate {m3/s}
    0.0055,                  !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n401,          !- Supply Air Fan Name
    Extraction_n401;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT2_sejour,            !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-02,         !- Heat Exchanger Name
    0.011,                   !- Supply Air Flow Rate {m3/s}
    0.011,                   !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n402,          !- Supply Air Fan Name
    Extraction_n402;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT3_sejour,            !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-03,         !- Heat Exchanger Name
    0.0055,                  !- Supply Air Flow Rate {m3/s}
    0.0055,                  !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n403,          !- Supply Air Fan Name
    Extraction_n403;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT3_chambre1,          !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-04,         !- Heat Exchanger Name
    0.0055,                  !- Supply Air Flow Rate {m3/s}
    0.0055,                  !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n404,          !- Supply Air Fan Name
    Extraction_n404;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT3_chambre2,          !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-05,         !- Heat Exchanger Name
    0.018,                   !- Supply Air Flow Rate {m3/s}
    0.018,                   !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n405,          !- Supply Air Fan Name
    Extraction_n405;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT3s_sejour,           !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-06,         !- Heat Exchanger Name
    0.00416,                 !- Supply Air Flow Rate {m3/s}
    0.00416,                 !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n406,          !- Supply Air Fan Name
    Extraction_n406;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT3s_chambre1,         !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-07,         !- Heat Exchanger Name
    0.00416,                 !- Supply Air Flow Rate {m3/s}
    0.00416,                 !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n407,          !- Supply Air Fan Name
    Extraction_n407;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT3s_chambre2,         !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-08,         !- Heat Exchanger Name
    0.00416,                 !- Supply Air Flow Rate {m3/s}
    0.00416,                 !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n408,          !- Supply Air Fan Name
    Extraction_n408;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT4_chambre3,          !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-09,         !- Heat Exchanger Name
    0.0166,                  !- Supply Air Flow Rate {m3/s}
    0.0166,                  !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n409,          !- Supply Air Fan Name
    Extraction_n409;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT4_sejour,            !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-10,         !- Heat Exchanger Name
    0.0055,                  !- Supply Air Flow Rate {m3/s}
    0.0055,                  !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n410,          !- Supply Air Fan Name
    Extraction_n410;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT4_chambre1,          !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-11,         !- Heat Exchanger Name
    0.0055,                  !- Supply Air Flow Rate {m3/s}
    0.0055,                  !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n411,          !- Supply Air Fan Name
    Extraction_n411;         !- Exhaust Air Fan Name

ZoneHVAC:EnergyRecoveryVentilator,
    DFnT4_chambre2,          !- Name
    DF_scenario,             !- Availability Schedule Name
    Echangeur_N4-12,         !- Heat Exchanger Name
    0.018,                   !- Supply Air Flow Rate {m3/s}
    0.018,                   !- Exhaust Air Flow Rate {m3/s}
    Soufflage_n412,          !- Supply Air Fan Name
    Extraction_n412;         !- Exhaust Air Fan Name


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:BASEBOARD:CONVECTIVE:ELECTRIC ===========

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T2_chambre,         !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T2_sejour,          !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3_sejour,          !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3_chambre1,        !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3_chambre2,        !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3s_sejour,         !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3s_chambre1,       !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3s_chambre2,       !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T4_chambre3,        !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T4_sejour,          !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T4_chambre1,        !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T4_chambre2,        !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T2_sdb,             !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3_sdb,             !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3_cuisine,         !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3s_cuisine,        !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3s_sdb,            !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T4_sdb,             !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T4_cuisine,         !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3_couloir,         !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T3s_couloir,        !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency

ZoneHVAC:Baseboard:Convective:Electric,
    Cvct_T4_couloir,         !- Name
    Always On,               !- Availability Schedule Name
    1000,                    !- Nominal Capacity {W}
    1;                       !- Efficiency


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTLIST ===========

ZoneHVAC:EquipmentList,
    ERVn401,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT2_chambre,           !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T2_chambre,         !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn402,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT2_sejour,            !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T2_sejour,          !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn403,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT3_sejour,            !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T3_sejour,          !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn404,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT3_chambre1,          !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T3_chambre1,        !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn405,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT3_chambre2,          !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T3_chambre2,        !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn406,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT3s_sejour,           !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T3s_sejour,         !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn407,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT3s_chambre1,         !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T3s_chambre1,       !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn408,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT3s_chambre2,         !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T3s_chambre2,       !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn409,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT4_chambre3,          !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T4_chambre3,        !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn410,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT4_sejour,            !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T4_sejour,          !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn411,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT4_chambre1,          !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T4_chambre1,        !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn412,                 !- Name
    ZoneHVAC:EnergyRecoveryVentilator,  !- Zone Equipment 1 Object Type
    DFnT4_chambre2,          !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1,                       !- Zone Equipment 1 Heating or No-Load Sequence
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 2 Object Type
    Cvct_T4_chambre2,        !- Zone Equipment 2 Name
    2,                       !- Zone Equipment 2 Cooling Sequence
    2;                       !- Zone Equipment 2 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn413,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T2_sdb,             !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn414,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T3_sdb,             !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn415,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T3_cuisine,         !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn416,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T3s_cuisine,        !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn417,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T3s_sdb,            !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn418,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T4_sdb,             !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn419,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T4_cuisine,         !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn420,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T3_couloir,         !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn421,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T3s_couloir,        !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence

ZoneHVAC:EquipmentList,
    ERVn422,                 !- Name
    ZoneHVAC:Baseboard:Convective:Electric,  !- Zone Equipment 1 Object Type
    Cvct_T4_couloir,         !- Zone Equipment 1 Name
    1,                       !- Zone Equipment 1 Cooling Sequence
    1;                       !- Zone Equipment 1 Heating or No-Load Sequence


!-   ===========  ALL OBJECTS IN CLASS: ZONEHVAC:EQUIPMENTCONNECTIONS ===========

ZoneHVAC:EquipmentConnections,
    T2 Chambre,              !- Zone Name
    ERVn401,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n401,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n401,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n401,      !- Zone Air Node Name
    Air_reprise_n401;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T2_Salon_Ouest,          !- Zone Name
    ERVn402,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n402,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n402,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n402,      !- Zone Air Node Name
    Air_reprise_n402;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Nord Sejour,          !- Zone Name
    ERVn403,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n403,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n403,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n403,      !- Zone Air Node Name
    Air_reprise_n403;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Nord Chambre 1,       !- Zone Name
    ERVn404,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n404,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n404,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n404,      !- Zone Air Node Name
    Air_reprise_n404;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Nord Chambre 2,       !- Zone Name
    ERVn405,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n405,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n405,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n405,      !- Zone Air Node Name
    Air_reprise_n405;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Sud Salon,            !- Zone Name
    ERVn406,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n406,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n406,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n406,      !- Zone Air Node Name
    Air_reprise_n406;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Sud Chambre 1,        !- Zone Name
    ERVn407,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n407,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n407,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n407,      !- Zone Air Node Name
    Air_reprise_n407;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Sud Chambre 2,        !- Zone Name
    ERVn408,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n408,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n408,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n408,      !- Zone Air Node Name
    Air_reprise_n408;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T4 Chambre 3,            !- Zone Name
    ERVn409,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n409,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n409,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n409,      !- Zone Air Node Name
    Air_reprise_n409;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T4 Salon,                !- Zone Name
    ERVn410,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n410,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n410,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n410,      !- Zone Air Node Name
    Air_reprise_n410;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T4 Chambre 1,            !- Zone Name
    ERVn411,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n411,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n411,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n411,      !- Zone Air Node Name
    Air_reprise_n411;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T4 Chambre 2,            !- Zone Name
    ERVn412,                 !- Zone Conditioning Equipment List Name
    Sortie_ventilateur_soufflage_n412,  !- Zone Air Inlet Node or NodeList Name
    Entree_echangeur_reprise_n412,  !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n412,      !- Zone Air Node Name
    Air_reprise_n412;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T2 SdB,                  !- Zone Name
    ERVn413,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n413,      !- Zone Air Node Name
    Air_reprise_n413;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Nord SdB,             !- Zone Name
    ERVn414,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n414,      !- Zone Air Node Name
    Air_reprise_n414;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Nord Cuisine,         !- Zone Name
    ERVn415,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n415,      !- Zone Air Node Name
    Air_reprise_n415;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Sud Cuisine,          !- Zone Name
    ERVn416,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n416,      !- Zone Air Node Name
    Air_reprise_n416;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Sud SdB,              !- Zone Name
    ERVn417,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n417,      !- Zone Air Node Name
    Air_reprise_n417;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T4 SdB,                  !- Zone Name
    ERVn418,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n418,      !- Zone Air Node Name
    Air_reprise_n418;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T4 Cuisine,              !- Zone Name
    ERVn419,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n419,      !- Zone Air Node Name
    Air_reprise_n419;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Nord Couloir,         !- Zone Name
    ERVn420,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n420,      !- Zone Air Node Name
    Air_reprise_n420;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T3 Sud Couloir,          !- Zone Name
    ERVn421,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n421,      !- Zone Air Node Name
    Air_reprise_n421;        !- Zone Return Air Node Name

ZoneHVAC:EquipmentConnections,
    T4 Couloir,              !- Zone Name
    ERVn422,                 !- Zone Conditioning Equipment List Name
    ,                        !- Zone Air Inlet Node or NodeList Name
    ,                        !- Zone Air Exhaust Node or NodeList Name
    Air_soufflage_n422,      !- Zone Air Node Name
    Air_reprise_n422;        !- Zone Return Air Node Name




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://docs.yahoo.com/info/terms/