|
Your “space101” is not assigned to any thermal zone You need to go to “facility” select “space 101” you will see no thermal zone assigned to it drag and drop your “thermal zone 1” Probably some other errors could exist you will discover it running again your file Josep Solé Sustainibility & Technical Manager Móvil +34 606 42 32 14 De: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] En nombre de Jaime Zuluaga Machado Hi everyone! i am beginner with the OpenStudio GUI, can you help me please?. Just i did was a 1 story building (very simple) and when i run the simulation, it did not work, the errors that it shows was: Program Version,EnergyPlus-Windows-OMP-32 7.2.0.006, YMD=2013.07.24 14:46,IDD_Version 7.2.0.006 ** Warning ** ManageSizing: For a zone sizing run, there must be at least 1 Sizing:Zone input object. SimulationControl Zone Sizing option ignored. ** Severe ** GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 1 ** Fatal ** GetSurfaceData: Errors discovered, program terminates. ...Summary of Errors that led to program termination: ..... Reference severe error count=1 ..... Last severe error=GetSurfaceData: Zone has no surfaces, Zone=THERMAL ZONE 1 ************* Warning: Node connection errors not checked - most system input has not been read (see previous warning). ************* Fatal error -- final processing. Program exited before simulations began. See previous error messages. ************* EnergyPlus Warmup Error Summary. During Warmup: 0 Warning; 0 Severe Errors. ************* EnergyPlus Sizing Error Summary. During Sizing: 1 Warning; 0 Severe Errors. ************* EnergyPlus Terminated--Fatal Error Detected. 1 Warning; 1 Severe Errors; Elapsed Time=00hr 00min 1.56sec Does anyone know what would happen? i do not know how to check the surfaces in thermal zone 1. any clue? BW: I attached the files. Jaime Zuluaga M __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |