The default value for number of iterations is 500. Have you tried increasing this or adjusting the convergence criteria? Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of Anisur Rahman Hi Bruno Scalet, Thanks again. I tried with INPUT option. But still it is giving the same error. Any further suggestion. Best Regards, PhD Candidate From: Bruno Scalet <bruno.scalet@xxxxxxxxx> Hello, I had the same problem today. As written in the I/O file, the AirflowNetwork object with "SurfaceAvarageCalculation" option in the field "Wind Pressure Coefficient Type" only supports simple
geometry (rectangular or squared ones). If your geometry/envelope is different from it you should use the option "Input" which will require all the pressure entries to this building you are modeling. I hope I've helped you. Greetings, Bruno Scalet __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.