Re: [EnergyPlus_Support] Revisiting SRI modeling and calculations





IMO spot on...solar = whole spectrum, thermal=ir specturm.
LEED has an official calculator to go from SRI to reflectance, i just can't remember where I spotted it.


On 23 August 2013 17:12, Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> wrote:
 

Dear Forum,

I thought I had this topic (modeling SRI values in E+) well understood, but now I am unsure.  Please let me know if the approach below is sound:

·         The technical data for a ?cool? roof generally notes solar reflectance and solar emittance along with an SRI value

·         EnergyPlus?s Material object wants to know thermal absorptance, solar absorptance and visible absorptance (plus other properties)

 

As far as I can tell,

1.       solar absorptance for E+ = 1 - solar reflectance from technical data

2.       thermal absorptance for E+ = solar emittance from technical data

3.       visible absorptance is anyone?s guess, since it?s not mentioned in the technical data.

 

Does that sound correct?  Thanks in advance!

 

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653




__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___