My understanding of the DesignBuilder implementation of air infiltration testing data is that the input is used to assign constant infiltration rates to each
zone of the building based on exterior area. The referenced standard is clear that this is a maximum infiltration to all zones intended for sizing heating equipment. It may not be doing what you want for a whole year energy simulation. If you want a whole year simulation, you need to create an AirflowNetwork model. I am working on the same thing for a larger building where I know my envelope
infiltration is different for the main building areas than it is for areas in and adjacent to the roof. I plan to define leakage rates for the perimeter of the windows and cracks in the attic such that total leakage equals my test leakage at a given pressure.
The AirflowNetwork should then be able to calculate infiltration based on weather file data. You can do the same from DesignBuilder and use CFD to assign pressure coefficients, but it is not as simple as just entering your test results to one input. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
On Behalf Of georgiou.geo13@xxxxxxxxx Dear group, I have carried out an infiltration test at a house and I want to upload the results on my model. However, when I developed the model I also include the basement of the building which is not taken in account during the infiltration test.
When I am setting the value in ACH at DesignBuilder, the basement is included. Does anybody know how can I set the value that I measured for the whole building to represent particular zones of the model? (DesingBuilder or EnergyPlus) Best Regards __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.