I solve the problem.
The problem is that my pumps was not sending enough water flow for fancoils. Thank you all!
Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor em Eficiência Energética LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx Date: Mon, 9 Sep 2013 06:21:45 -0500 Subject: RE: [EnergyPlus_Support] Controller Error On further reflection, it appears that your chilled water system is not ON ? the water temperature is 26C!
James V Dirkes II, PE, BEMP, LEED AP
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Jim Dirkes
Respectfully disagreeing ?. HVAC Cooling coils are always reverse action. This is specified in the Controller:WaterCoil object (example below). I do not recall all of the several ways that I have erred in order to receive this message, but I think improper setpoints are the most common. Your 12.8C setpoint looks OK, but perhaps there is a zone setpoint that is improper?
James V Dirkes II, PE, BEMP, LEED AP
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of Alberto Hernandez Neto - USP
Dear Ivan,
You should change the status of reverse action of the colling coil controller .
Regards,
Alberto Hernandez Neto
De: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Em nome de Ivan Mezzacapa
Hi!
i don't know how solve this problem. Someone could help me?
Thanks!!
** Severe ** FindRootSimpleController: Controller error for controller = "FC-3P-A-01 COOLING COIL CONTROLLER" ** ~~~ ** Environment=Sao Paulo -TRY WMO#=, at Simulation time=01/16 08:00 - 08:15 ** ~~~ ** Controller function is inconsistent with user specified controller action = "" action ** ~~~ ** Actuator will be set to maximum action ** ~~~ ** Controller control type=Temperature ** ~~~ ** Controller temperature setpoint = 12.80 [C] ** ~~~ ** Controller sensed temperature = 25.78 [C] ** ~~~ ** Controller actuator mass flow rate set to 4.27 [kg/s] ** ~~~ ** Controller actuator temperature = 26.10 [C] ** ~~~ ** Note: Chilled water coils should be reverse action and the entering chilled ** ~~~ ** water temperature (controller actuator temperature) should be below the setpoint temperature ** ~~~ ** Note: Hot water coils should be normal action and the entering hot ** ~~~ ** water temperature (controller actuator temperature) should be above the setpoint temperature
Técg. Ivan Mezzacapa Projetista de Ar Condicionado / Consultor em Eficiência Energética LinkedIN: http://www.linkedin.com/in/ivanmezzacapa Facebook: http://www.facebook.com/ivan.mezzacapa Celular: (11)9963-9326 __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.