[EnergyPlus_Support] What should Heat Rejection reasonable value be?



Hi,
I have done a simulation for a project and I got these results for baseline:
Cooling = 830,787.3 [kWh/year]
Heat Rejection = 50,417.5 [kWh/year]


My question is: 
Shouldn't the Heat Rejection value be greater than Cooling? because what I remember from Thermodynamics is Qh=Ql+W
So, the heat rejection should be equal to the heat pumped out of spaces + the energy consumed in the compressor, right?


If the above discussion is correct, what could I have done wrong? because I modeled the HVAC system as System 8: Water cooled chiller and VAV with PFP boxes(ASHRAE 90.1-2007 Appendix G) by putting the following HVACTemplate Objects:
1. Thermostat.
2. Zone:VAV:FanPowered.
3. System:VAV.
4. Plant:ChilledWaterLoop.
5. Plant:Chiller.
6. Plant:Tower.
I couldn't find where to define that the cooling tower is connected to the chiller, so I assumed this is done automatically in HVACTemplate method, right?


Thank you.
--
Hisham




------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx 
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo! Groups is subject to:
    http://info.yahoo.com/legal/us/yahoo/utos/terms/