[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Re: Using AFN for windows, but with default infiltration
- To: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Subject: [EnergyPlus_Support] Re: Using AFN for windows, but with default infiltration
- From: "allinson_louis" <allinson_louis@xxxxxxxxxxx>
- Date: Mon, 07 Oct 2013 07:59:07 -0000
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Mon, 07 Oct 2013 07:04:22 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1381151062; bh=BTZAI7GvqVlyOFg9gLKDh6EULqNI608L9+UMyR72MUk=; h=Received:Received:X-Yahoo-Newman-Id:Received:Received:Received:Received:DKIM-Signature:Received:Received:Received:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:Message-ID:In-Reply-To:User-Agent:X-Mailer:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:X-Yahoo-Profile:To:X-eGroups-Approved-By:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:Content-Transfer-Encoding; b=19ZZYUgx4ITB5lvMSqQWmEP32p+hjjLAOD9WIK10TMkNEQCVmxLSgSz6MKAIU/lnLlgRSwK346sBsK5V4FVbLfIlvaRyMJRsfsVMT3TDVDzlHLeluB8z3AQg0Ko7fPPwF+6AhgfF10yKN+tcyJNfWMjvJLS9wK/unSo8oP5Jkuk=
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1381151061; bh=8UWcJ1zgqYysx0vOKRJ75EcnxMesMt2PQkXY+QSXiwQ=; h=Received:Received:Received:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:Date:Message-ID:In-Reply-To:User-Agent:MIME-Version:Content-Type:Content-Transfer-Encoding:X-Mailer:X-Yahoo-Newman-Property:X-Originating-IP:X-eGroups-Msg-Info:X-Yahoo-Post-IP:From:Subject:X-Yahoo-Group-Post:X-Yahoo-Profile:X-YGroups-SubInfo:To:Sender:X-Yahoo-Newman-Property:X-Yahoo-Newman-Id:X-eGroups-Approved-By:X-eGroups-Auth; b=qMvvgl5lhIr5ZGAb8RihggyQST5Q4JFd25LsW7U5/aZjnoIsAVyUD9TBxI00xTcKai4B2AJ8dQVOsJt00mXZ14Rt1Z9p20YCuKf/QsqwvEocVGMjLsZweuORPAD8gODr1IJrLdT/9Kw9KgbZzDjF3/4ROfTxF0YuW8IOXaRGAKY=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=rNQW4sPp9C3iFeYINW/u0AXuAUyL6fHcH5RbrQXQP+CVgZohPKNE7MM+Xv9r9aN9vRz30IvkZyhiUbOgj2z+FqPeh9Ky+tdoYbmnm4HI5LgOkic8QIX6frSvPfWLmunTTAZoU7fyWqWiWTyMUVpWMb2BuhBQ5v2F00hyeN3WZgI=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- In-reply-to: <7AFDF9AE-5839-4A9D-90F4-8581739485CF@gmail.com>
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
- Sender: EnergyPlus_Support@xxxxxxxxxxxxxxx
- User-agent: eGroups-EW/0.82
Thank you for this informative post. Plenty of food for thought. I was just wanting to ensure my model was 'equivalent' to other models I had seen (not using e+) which tend to model a standard 0.1ach as an assumption
which of course does not represent reality but apperas to be a typical assumption
--- In EnergyPlus_Support@xxxxxxxxxxxxxxx, "jeannieboef@..." <jeannieboef@...> wrote:
>
> Just saying a big "YES!" to Joe's comments.
>
> Extra points are:
> 1) You could pretend there was a blower door test and ASSUME all leaks
> in the closed possition are equally leaky per linear length. That
> means measuring out all your modelled exterior facing leaks (example
> top bottom sides of all modelled doors and windows). This allows you
> to calculate the "per meter length leakage coefficient at 50 Pa for
> example that is required for a desired air change for your facility by
> using the normal power-law equation (Q = C*dP^n). Note that you'll
> have to sum the total volume of the facility to convert the required
> ACH to m3/s for the power-law equation. After you have calculated C
> (assume C is the same at 1 Pa as at 50 Pa), you can place this same
> input on each exterior leak object as discussed. This is currently my
> prefered method for using AFN where a lot of assumptions must be made.
>
> 2) Data-driven approaches aren't wrong as such. The downside is that
> you rely heavily on the statistics you put to ground. For example, if
> you have statistical infiltration data for 100 builings of similar
> type and hvac to yours in your climate, then this is a viable option
> for you, if you can live with the granularity of the data. In my
> opinion this method should be used (normal infiltration objects) for
> most mechanically ventilated buildings (opening events are usually far
> less and at times where large temperature swings are unlikely). Where
> I start getting irritated is using data-driven approaches to only-
> window-ventilated buildings. The temperature swings and number of
> venting occurances are huge and seriously affect user comfort, which
> in turn effects the opening and closing of the windows --> heating of
> outdoor air and energy consumption. The minute-wise data just isn't
> there.
>
> 3) A third approach is possibly the best. A data-driven approach with
> stoastic modelling of the main factors which lead to when and for how
> long a widow stays open (Anderson)...these factors would be inputs
> into a formula which would open or close the window on a probability
> threshold coupled to a randomness effect. Inputs which would increase
> or decrease this probability are the usual:
> Temperature zone
> Temperature of outdoor air
> Time of year
> Solar
> Stuffiness of air possibly using CO2 as an indicator
> Number of people in the zone
> Number of people having entered the zone to stay in the zone from the
> last timestep
> Room air velocity or windvelocity
> Etc.
>
> 4) I've tried a bit of an advanced version of 1) (AFN + EMS control
> algorithm for x2 widow groups, based on monitoring comfort criteria)
> approach based mainly on PPD threshholds of comfort criteria including
> CO2. The only thing I kept constant were that the persons in my
> facility were evenly distributed (no human traffic modelling), but the
> densities were indeed scheduled. It worked quite well to identify
> problems with the design and possible solutions and demonstrated
> typical expected CO2 concentrations for my design. It also showed the
> problem that windows don't linearly modulate (even when split into two
> independant groups per zone)...this means that occupants close windows
> too quickly after the opening event in winter due to "cold draughts"
> or intense temperature swings in the space. My model required 1 minute
> timesteps to catch this effect. It also showed up the common problem
> of controlling a heating system which is based on an air temperature
> thermostat. I like this approach best, but would idealy prefer the PPM
> threshholds still to be affected by an element of randomness and to
> include the human traffic element (the most significant ones being the
> venting upon the entry of a new person who is likely to stay AND the
> venting of unoccupied rooms). My other significant assumption was
> imposing a limit on the opening event frequency (not closing). I found
> no data to base this assumption on.
>
> Hopefully there was some food for thought in my rambles.
>
>
> Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity)
>
> i. A.
> Jean Marais
> b.i.g. bechtold
> Tel. +49 30 6706662-23
>
> On 03.10.2013, at 19:21, Joe Huang <YJHuang@...>
> wrote:
>
> > I'm afraid you're missing the point.�� The original
> > question was how to model infiltration when the AFN is being used.
> > My point was that you cannot mix the infiltration object in
> > conjunction with the AFN.�� If you want to model
> > infiltration with the AFN, you have to define the leakage characteri
> > stics of the space for the AFN�� (this should probably be
> > done anyway for proper modeling - in fact, all these AFN programs su
> > ch as COMIS and AirNet were originally designed not for modeling nat
> > ural ventilation, but rather infiltration).��
> >
> > Sure, you can use a blower door test to get the leakage fraction,
> > but that has to be used as an input to the AFN, not to the
> > infiltration object.���� I've always been adverse
> > to modeling infiltration as a constant air change rate, because that
> > 's nonphysical and not what really happens.�� IMHO, it's
> > always much better to define the physical characteristics of the spa
> > ce (leakage-fraction, area of cracks, etc.) and then use a physical
> > model like the Sherman-Grimsrud or the AFN to then compute the hour-
> > to-hour infiltration.
> >
> > Joe
> > Joe Huang
> > White Box Technologies, Inc.
> > 346 Rheem Blvd., Suite 108D
> > Moraga CA 94556
> > yjhuang@...
> > http://weather.whiteboxtechnologies.com for simulation-ready weather
> > data
> > (o) (925)388-0265
> > (c) (510)928-2683
> > "building energy simulations at your fingertips"
> >
> > On 3/10/2013 9:25 AM, Oscar Hernandez wrote:
> >>
> >> There are many methods to calculate the real infiltration
> >> value...like the blower test.
> >>
> >> On Oct 3, 2013 6:06 PM, <josep.sole@...> wrote:
> >> ��
> >> In AFN models you need to assume a lot of other hypothesis it is no
> >> easier than assume the zone infiltration rate.
> >>
> >>
> >> ��
> >>
> >> Josep Sol��
> >> URSA Insulation S.A-
> >>
> >> Sustainibility & Technical Manager��
> >>
> >> M��vil +34 606 42 32 14
> >>
> >> www.ursa.es
> >>
> >> www.ursainsulation.com
> >>
> >> www.uralita.com
> >>
> >> ��<mime-attachment.gif>
> >> P URALITA / URSA se compromete con el ahorro de energ��a.
> >> Antes de imprimir este mensaje aseg��rese de que es necesar
> >> io.
> >>
> >> ��
> >>
> >> De: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >> [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] En nombre de Oscar
> >> Hernandez
> >> Enviado el: jueves, 03 de octubre de 2013 17:57
> >> Para: EnergyPlus_Support@xxxxxxxxxxxxxxx
> >> Asunto: Re: [EnergyPlus_Support] Using AFN for windows, but with
> >> default infiltration
> >>
> >> ��
> >>
> >> ��
> >>
> >> If you want to model an infiltration value use the zone
> >> infiltration. The AFN its to predict the infiltrattion value when
> >> you don"t know it.
> >>
> >> ��
> >>
> >> On 3 October 2013 17:42, Joe Huang
> >> <YJHuang@...> wrote:
> >>
> >> ��
> >>
> >> I don't think the infiltration objects can be used in conjunction
> >> with the AFN. That would violate the mass balance of the AFN,
> >> wouldn't it?
> >>
> >> Sent from my IPad
> >>
> >> ��
> >>
> >> Joe Huang
> >>
> >> ��
> >>
> >>
> >> On Oct 3, 2013, at 8:35 AM, Oscar Hernandez <eng.ohw@...>
> >> wrote:
> >>
> >> ��
> >>
> >> Hi,
> >>
> >> Use the zone infiltration.
> >>
> >> Oscar
> >>
> >> On Oct 3, 2013 2:48 PM, "allinson_louis"
> >> <allinson_louis@...> wrote:
> >>
> >> ��
> >>
> >> Hi All
> >>
> >> I am using AFN to model air flow through window openings that I am
> >> controlling using EMS
> >>
> >> However, when the windows are closed the only infiltration is
> >> through cracks and the infiltration is much less than 0.1ach. I
> >> want to model a 'default' 0.1ach when the windows are closed, as
> >> this is a typical value used in simulations.
> >>
> >> Is this possible?
> >>
> >> ��
> >>
> >
>
------------------------------------
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Yahoo! Groups Links
<*> To visit your group on the web, go to:
http://groups.yahoo.com/group/EnergyPlus_Support/
<*> Your email settings:
Individual Email | Traditional
<*> To change settings online go to:
http://groups.yahoo.com/group/EnergyPlus_Support/join
(Yahoo! ID required)
<*> To change settings via email:
EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
<*> To unsubscribe from this group, send an email to:
EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
<*> Your use of Yahoo! Groups is subject to:
http://info.yahoo.com/legal/us/yahoo/utos/terms/