Time for me to ask a question. I want to take the ventilation rate from another program and feed it into EnergyPlus without any modifications. Looking through the IDD, it seems I can do this using either the ZoneInfiltration:DesignFlowRate or the ZoneVentilation:DesignFlowRate object, but in either case I would have to disable the temperature and velocity coefficients by setting them to 0, leaving the constant term as 1.0. Likewise, I would use flow/zone as the calculation "method" with the rate set to 1.0. Does anyone see any problem in doing this, and whether there is any difference between the two objects when used in this manner ? Thanks for any comments or suggestions. Joe Joe Huang White Box Technologies, Inc. 346 Rheem Blvd., Suite 108D Moraga CA 94556 yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx http://weather.whiteboxtechnologies.com for simulation-ready weather data (o) (925)388-0265 (c) (510)928-2683 "building energy simulations at your fingertips" __._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.