I've already tried to use one of the dataset g-functions but they gave me some problems...
Program Version,EnergyPlus-Windows-OMP-64 7.2.0.006, YMD=2013.11.01 17:55,IDD_Version 7.2.0.006
************* Beginning Zone Sizing Calculations
** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.
** ~~~ ** These values may be inappropriate. Please consult the Input Output Reference for more details.
** Warning ** CheckUsedConstructions: There are 4 nominally unused constructions in input.
** ~~~ ** Each Unused construction is shown.
************* Construction=CONSTGLZ7580
************* Construction=CONSTGLZ5679
************* Construction=CONSTGLZ4471
************* Construction=CONSTGLZ3045
************* Beginning Plant Sizing Calculations
** Severe ** GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.
** ~~~ ** ...Pipe Thickness=[998.200].
** ~~~ ** ...Pipe Out Diameter=[0.389].
** ~~~ ** ...Radius will be <=0.
** Warning ** GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.
** ~~~ ** ...Maximum Length of Simulation less than RunPeriod Request
** ~~~ ** Requested input=0 will be set to 1
** Fatal ** Errors found in processing input for GroundHeatExchanger:Vertical
...Summary of Errors that led to program termination:
..... Reference severe error count=1
..... Last severe error=GroundHeatExchanger:Vertical="VERTICAL GROUND HEAT EXCHANGER", invalid value in field.
************* Warning: Node connection errors not checked - most system input has not been read (see previous warning).
************* Fatal error -- final processing. Program exited before simulations began. See previous error messages.
*************
************* =
On Fri, Nov 1, 2013 at 10:33 AM, <silvia1-@...> wrote:Hi, I'm a student and I don't have GSHE-Pro but I need a G-function for my research on energy efficiency measures and I want ask if someone can generate for me a G-function specific for my building? Thanks
--Edwin Lee, PhDEngineer, Commercial Buildings Research StaffNational Renewable Energy Laboratory