Silvia,

I think the source side is the ground loop.  The load side should be your radiant floor.

Have you checked your flows?  Are they as you specified?  If autosized, are the flows consistent with your other criteria like temperature difference?

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of silvia1-@xxxxxxxxxx
Sent: Wednesday, November 06, 2013 1:48 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] RE: Error: Saturation temperature is out of range

 

 

To Jim Dirkes 

 

What you are saying means that the heat pump and the ground heat exchanger (source-side) are not enough powerfull to respond to the radiant floor demand (load-side)... am I right? 



---In energyplus_support@xxxxxxxxxxxxxxx, <curtis@...> wrote:

Someone having GSHP fun in EnergyPLus�..

 

Robin

 

 

On 6 Nov 2013, at 12:17, silvia1-@... wrote:



 

 

(It is a radiant floor model with GSHP)

 



---In EnergyPlus_Support@xxxxxxxxxxxxxxx, <silvia1-@...> wrote:

CAN SOMEONE TELL ME HOW TO FIX THIS PROBLEMS? WHICH PARAMETERS I SHOULD TRY TO CORRECT?

 

Program Version,EnergyPlus-Windows-OMP-64 7.2.0.006, YMD=2013.11.06 12:51,IDD_Version 7.2.0.006

   ************* Beginning Zone Sizing Calculations

   ** Warning ** Site:GroundTemperature:BuildingSurface: Some values fall outside the range of 15-25C.

   **   ~~~   ** These values may be inappropriate.  Please consult the Input Output Reference for more details.

   

   ** Severe  ** GetSatPressureRefrig: Saturation temperature is out of range for refrigerant [R22] supplied data: **

   **   ~~~   ** ...Called From:CalcGSHPModel:LoadSideTemp

   **   ~~~   ** ...Supplied Refrigerant Temperature=97.88 Returned saturated pressure value = 4990000

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=03/08 16:20 - 16:30

   ** Severe  ** GetInterpolatedSatProp: Saturation temperature for interpolation is out of range of data supplied: **

   **   ~~~   **  Called from:CalcGSHPModel:LoadSideTemp Environment=TUMYIL=ALLYEAR, at Simulation time=03/08 16:20 - 16:30

   **   ~~~   ** Refrigerant temperature = 97.88

   **   ~~~   ** Returned saturated property value = 366900.000

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/02 11:00 - 11:05

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 0.258699470296460

   **   ~~~   ** Load-side heat transfer rate   = 32069.0592942236

   **   ~~~   ** Source-side heat transfer rate = 11691.8595678346

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.132869306612469

   **   ~~~   ** Source-side inlet temperature  = 13.6019709760082

   **   ~~~   ** Load-side inlet temperature    = 36.0222114867705

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/02 11:10 - 11:20

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 5.93580823996133

   **   ~~~   ** Load-side heat transfer rate   = 32028.2246123877

   **   ~~~   ** Source-side heat transfer rate = 11358.6307785808

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.126268293876080

   **   ~~~   ** Source-side inlet temperature  = 13.5948762109171

   **   ~~~   ** Load-side inlet temperature    = 36.8916394885419

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/13 09:00 - 09:10

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 3.12417095891493

   **   ~~~   ** Load-side heat transfer rate   = 29070.1690729848

   **   ~~~   ** Source-side heat transfer rate = 8752.16631028519

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.124107062123656

   **   ~~~   ** Source-side inlet temperature  = 12.9295336405605

   **   ~~~   ** Load-side inlet temperature    = 38.3275434761950

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/16 10:10 - 10:13

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 4.78675132961050

   **   ~~~   ** Load-side heat transfer rate   = 28843.3575791721

   **   ~~~   ** Source-side heat transfer rate = 8646.07742895907

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.124664353230092

   **   ~~~   ** Source-side inlet temperature  = 12.8242422573327

   **   ~~~   ** Load-side inlet temperature    = 38.0458793375358

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/16 10:17 - 10:20

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 0.321941627674593

   **   ~~~   ** Load-side heat transfer rate   = 30127.2475159258

   **   ~~~   ** Source-side heat transfer rate = 9911.38377908106

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.127463450923846

   **   ~~~   ** Source-side inlet temperature  = 12.8230604638162

   **   ~~~   ** Load-side inlet temperature    = 38.6513070926305

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/16 10:25 - 10:30

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 3.71313018140605

   **   ~~~   ** Load-side heat transfer rate   = 28912.6820316747

   **   ~~~   ** Source-side heat transfer rate = 8677.87077772418

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.126515142130828

   **   ~~~   ** Source-side inlet temperature  = 12.8139942970623

   **   ~~~   ** Load-side inlet temperature    = 39.3706102810987

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/17 08:30 - 08:35

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 3.21145625715503

   **   ~~~   ** Load-side heat transfer rate   = 29165.7858900555

   **   ~~~   ** Source-side heat transfer rate = 8796.19788136824

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.121461505892438

   **   ~~~   ** Source-side inlet temperature  = 13.0349029932632

   **   ~~~   ** Load-side inlet temperature    = 36.8493583126320

   ** Warning ** HeatPump:WaterToWater:ParameterEstimation:Heating did not converge

   **   ~~~   **  Environment=TUMYIL=ALLYEAR, at Simulation time=10/24 13:30 - 13:40

   **   ~~~   ** Heatpump Name = GSHPHEATING

   **   ~~~   ** Heat Inbalance (%)             = 7.710154152471915E-002

   **   ~~~   ** Load-side heat transfer rate   = 31474.7772762660

   **   ~~~   ** Source-side heat transfer rate = 11837.4572323483

   **   ~~~   ** Source-side mass flow rate     = 29.9969400000000

   **   ~~~   ** Load-side mass flow rate       = 0.151677828531309

   **   ~~~   ** Source-side inlet temperature  = 12.3668697825035

   **   ~~~   ** Load-side inlet temperature    = 43.1189682428199

 

 



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___