[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Node connection error





You have zone inlet node (SPACE4-1 In Node) specified in the in a Zone Inlet NodeList "SPACE4-1 In Nodes" but not defined/used any where else. Remove/comment out the node "SPACE4-1 In Node" from the list.

Only one splitter is allowed in "AirLoopHVAC:SupplyPath".  You have unused splitter but defined in the idf.  Comment out the unused "Zone Supply Air Splitter 1" object.

These two correction will remove the sever errors.

Bereket


On Sunday, December 8, 2013 12:18 AM, Jeremiah Crossett <jcrossett@xxxxxxxxxxxxxxx> wrote:
 
I copied the heat pump water heater info into a file and modified a bit.  Everything looks correct, but it crashes and does not give any good clues to solve the problem.. 

If anyone could take a look at the node connections and let me know what I am doing wrong it would be appreciated. 




Jeremiah D. Crossett  | Senior Analyst  |  Phase Change Energy Solutions
120 E. Pritchard St.  | Asheboro, NC 27203 
 | Mobile 503-688-8951
  







__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___