Yes. Your idea is correct...are you quite new to e+? Check out the examples in the example folder. There is a thermostat object called something like thermostat:duelsetpoint...that's what you want. A thermostat object referances a schedule that you must define. That schedule holds values that represent the temperature setpoint values at which heating will kick in (cooling setpoint schedule is seperate and is seperately defined). Conceptually, it is only against these setpoints and the current zone air temperature that the programs calculates the heating or cooling loads on the zone. That is the normal setup. It should be noted (as previously mentioned by me) that the radiant object has another totally seperate setpoint schedule(s) which it referances and uses (but it could referance the same as those of the thermostat). Mit freundlichen Grü�en- Sent from my iPhone (excuse the brevity) i. A. Jean Marais b.i.g. bechtold Tel. +49 30 6706662-23
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.