[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Calculated design cooling load for zone is zero.





You also may want to set variables for your zone temp, cooling setpoint, and heating setpoint to see if you are actually exceeding these limits with your cooling coil at 0 design.  If you have a storage space that generates no load and is an interior zone as well as on a setback schedule then the cooling load will probably be zero.  Next, try reducing your inputs to the cooling coil one by one and see which of them is causing the dewpoint warning.  I'd start with the Wair,out first.


John Grando



__._,_.___


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required)
Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured
Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe

__,_._,___