It worked!!! Just to share with you, follow attached the grafics with outdoor during unocupied hours and bellow the zero outdoor air during unoccupied hours. Thanks Jim! To: EnergyPlus_Support@xxxxxxxxxxxxxxx From: jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx Date: Tue, 28 Jan 2014 09:24:30 -0600 Subject: RE: [EnergyPlus_Support] Night cycle Operation Fabiano, I think this will accomplish your goal. The ?Minimum Outdoor Air Schedule Name? is the same as the fan schedule, so for all unoccupied hours its value = 0.
James V Dirkes II, PE, BEMP, LEED AP
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] On Behalf Of fabianoferreira27@xxxxxxxxxxx
Hi everyone,
I would like to know how to model the HVAC system with zero outside airflow when the fans are cycled on to meet unoccupied setback temperatures operate? I've modeled fan to work to cycle on, but I?ve noticed that the outside airflow is working with the fan, grafic attached.
Thanks,
Fabiano Ferreira
__._,_.___ Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
Your email settings: Individual Email|Traditional
Change settings via the Web (Yahoo! ID required) Change settings via email: Switch delivery to Daily Digest | Switch to Fully Featured Visit Your Group | Yahoo! Groups Terms of Use | Unsubscribe __,_._,___ |
Attachment not found: C:\Users\lklawrie\Downloads\Embedded\image00332.png