Re: [EnergyPlus_Support] Outdoor Air Mixing Boxes




Did you then edit the .expidf file? Look at your IDF and see if these Output:Preprocessor objects are still in there and if you are not using HVACTemplate objects, delete the Output:Preprocessor objects.

Or, you are still using HVACTemplate and you don't know it.



On 2014-02-07 16:34, Sankey, Maxim L wrote:
Hi Everyone,

Is it possible to include two OA mixing boxes in a single air loop?

I'm getting an error that I think may be caused by including two oa
mixing boxes in a single loop. I began my system using the templates.
I created a dedicated outdoor air system (that didn't serve any zones)
so I could later combine it with another air loop. After expanding the
idf and combining the air loops, I am getting an error:

 ** Severe  ** Output:PreprocessorMessage="ExpandObjects" has the
following Fatal conditions:
   **   ~~~   ** You must specify at least one
   **   ~~~   **
HVACTemplate:Zone:FanCoil/PTAC/PTHP/WaterToAirHeatPump served by a
   **   ~~~   ** HVACTemplate:System:DedicatedOutdoorAir. Did not
find of match for ERU
   ** Severe  ** Output:PreprocessorMessage="ExpandObjects" has the
following Fatal conditions:
   **   ~~~   ** You must specify at least one
   **   ~~~   **
HVACTemplate:Zone:FanCoil/PTAC/PTHP/WaterToAirHeatPump served by a
   **   ~~~   ** HVACTemplate:System:DedicatedOutdoorAir. Did not
find of match for ERU

This doesn't make sense to me since I am not using templates anymore,
and I essentially got rid of the ERU dedicated outdoor air unit.

Any help would be appreciated, especially the first question above.




Maxim



------------------------------------

Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone
has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under
the Documentation link and press the "search" button.
Yahoo Groups Links

<*> To visit your group on the web, go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/

<*> Your email settings:
    Individual Email | Traditional

<*> To change settings online go to:
    http://groups.yahoo.com/group/EnergyPlus_Support/join
    (Yahoo! ID required)

<*> To change settings via email:
    EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
    EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx

<*> To unsubscribe from this group, send an email to:
    EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx

<*> Your use of Yahoo Groups is subject to:
    http://info.yahoo.com/legal/us/yahoo/utos/terms/