[EnergyPlus_Support] Zone Heating Design Supply Air Temperature Difference is not respected




Iâ??m modeling a baseline system according to Annex G of ASHRAE 90.1-2007. Paragraph G3.1.2.8 states that the â??system design supply airflow rates (..) shall be based on a supply-air-to-room-air temperature difference of 11°Câ??. In the case that Iâ??m modeling there is no outdoor air ventilation. I have imposed that statement through the fields â??Zone Cooling Design Supply Air Temperature Differenceâ?? and â??Zone Heating Design Supply Air Temperature Differenceâ?? of the object Sizing:Zone, as you can see in the following picture: <https://imageshack.com/i/nf55zcj>https://imageshack.com/i/nf55zcj

Iâ??m seeing the output graphs for the design day. Here the zone temperature for the winter design day (the setpoint temperature is equal to 20°C during the diurnal hours and itâ??s met): <https://imageshack.com/i/7gb2q5j>https://imageshack.com/i/7gb2q5j

That zone is conditioned by System 6 ? Packaged VAV with Parallel Fan Powered boxes.

The supply air temperature should be equal to 20°C + 11°C = 31 °C. In the following graph the temperature of the â??Outlet Node Nameâ?? of the object AirTerminal:SingleDuct:ParallelPIU:Reheat is plotted. You can see that that temperature is less than 31°C: <https://imageshack.com/i/0k4d2dj>https://imageshack.com/i/0k4d2dj

On the other hand, the supply air temperature is too high during the summer design day.

Can I consider the model autosized correctly according to Appendix G?



__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31317/stime=1392801657>

<http://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJldmVnOTVnBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5MjgwMTY1Nw-->Visit Your Group
* <http://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmaTB1am1oBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTI4MDE2NTc-?o=6>New Members 8
<http://groups.yahoo.com/;_ylc=X3oDMTJkZnE4N2R1BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzkyODAxNjU3><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <http://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <http://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___