Wouldn't that foul up the zone heat balance that depends on knowing the view factor or at least the area of each surface ?
Joe
On 2/19/2014 12:37 PM, Jeremiah Crossett wrote:
Depending on what you are doing, you might just as well ignore it-- for example if you want the surface to be fully adiabatic then you could remove it, and would get this warning.I have some models that are just roofs with zone area, ceiling height and internal loads per square foot-- and it seems to work as expected, but also produces this warning-
Jeremiah D. Crossett | Senior Analyst | Phase Change Energy Solutions120 E. Pritchard St. | Asheboro, NC 27203| Mobile 503-688-8951
On Wed, Feb 19, 2014 at 12:33 PM, Joe Huang <YJHuang@xxxxxxxxxxxxxxxxxxxxxxxx> wrote:
"Degenerate surfaces" sound terrible! Maybe you should go see a psychologist (just joking :-) )
Seriously, I suggest you search through your IDF, find the seven surfaces with less than two vertices (which only define a line and not a surface), and add the missing vertices.
Joe
On 2/19/2014 11:58 AM, Oswaldo alonso Guzmán villalobos wrote:
Hellow, I try to simulate a building, when I simulate it, the energy plus gives the following message,
GetSurfaceData: There are 7 degenerate surfaces; Degenerate surfaces are those with number of sides < 3.
How fix this error?Thanks.
Att. Oswaldo Alonso Guzmán Villalobos