So I was trying to use HAMT for moisture calculation in a single zone model consists of two sub-zones separated by a virtual wall (I used Material:InfraredTransparent object to accomplished this). Since this virtual wall is not a real wall and it is only there to separate my initial zone into two subzones due to their thermal load differences.
For exterior walls, floor, and roof I used the MoistureMaterials.idf in Reference DataSets. However, when I got to specify the moisture settings in MaterialProperty:HeatAndMoistureTransfer for the Virtual Wall that used IR Transparent Object as said, I had repeatedly severe errors in the ouput. Below is the severe error:
 ** Severe  ** InitCombinedHeatAndMoistureFiniteElement: Construction=AIR WALL
 **   ~~~   ** Reference Material="IRTMATERIAL" is too thin.
Note: Air Wall is my construction object for the virtual wall that used IRTMaterial specified in Material:InfraredTransparent
It looks like the problem is with the thickness of the IRMaterial. But I have no option to change the thickness of it in Material:InfraredTransparent.
Any suggestions or comments will be greatly appreciated.
Thanks,
Long

__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31494/stime=1394577627>

<https://groups.yahoo.com/group/EnergyPlus_Support;_ylc=X3oDMTJlNmVvcG1oBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5NDU3NzYyNw-->Visit Your Group
* <https://groups.yahoo.com/group/EnergyPlus_Support/members;_ylc=X3oDMTJmMmV2aHY1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTQ1Nzc2Mjc-?o=6>New Members 13
<https://groups.yahoo.com/;_ylc=X3oDMTJkcWgzaXFvBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk0NTc3NjI3><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___