Hi Jean,
unfortunately I haven't read about the object you mentioned yet. I forgot to report the severe error pointed by e+ during the idf simulation. It shows me a list of severe errors like these:

   ** Severe  ** Node REHEAT INLET SUPPLY NODE RECP0A1 connects to no component
   **   ~~~   ** Occurs in Supply Air Path=AIR LOOP DEMAND SIDE SUPPLY PATH 1
   **   ~~~   ** Check the connection to a ZoneHVAC:EquipmentConnections object
   **   ~~~   ** Check if this component is missing from the Supply Air Path
   ** Severe  ** Node REHEAT INLET SUPPLY NODE RECP0A2 connects to no component
   **   ~~~   ** Occurs in Supply Air Path=AIR LOOP DEMAND SIDE SUPPLY PATH 1
   **   ~~~   ** Check the connection to a ZoneHVAC:EquipmentConnections object
   **   ~~~   ** Check if this component is missing from the Supply Air Path
   ** Severe  ** Node REHEAT INLET SUPPLY NODE RECP0A3 connects to no component
   **   ~~~   ** Occurs in Supply Air Path=AIR LOOP DEMAND SIDE SUPPLY PATH 1
   **   ~~~   ** Check the connection to a ZoneHVAC:EquipmentConnections object
   **   ~~~   ** Check if this component is missing from the Supply Air Path
... and so on.

Maybe I forgot to link something, but as I said before, I'm not really expert and first of all, I would like to listen to your indications.

Thanks,
Marco

On Tuesday, April 22, 2014 10:08 AM, Jean Marais <jeannieboef@xxxxxxxxx> wrote:

Hi Marco,
I've never seen anyone on the forum try this. I'm not sure this object can be put on non-supplyside branches, i.e. I don't think it will work. I suspect this, because this object ties in closely with controller:outdoorair (i.e. the outdoor air mixing damper) and economizer function. I think you'll have to look for another object for the job. Perhaps the ZoneHVAC:EnergyRecoveryVentilator?


2014-04-22 9:52 GMT+02:00 <<mailto:m.aldegheri@xxxxxxxxx>m.aldegheri@xxxxxxxxx>:
>  
Dear all,
> 
> I would like some information about the HeatExchanger:AirToAir:SensibleAndLatent.
> 
> I have a mec vent network for a residential building.
> 
> At the moment the modeled network is the one shown in the svg I uploaded and I created it via DesignBulder.
> 
> But each flat in this building has an heat exchanger. In this way I should change the original network dividing the air flux in branches, one for each flat, and inserting in each of them an heat exchanger.
> 
> Now, my idea is to create one splitter and one mixer for each flat and put the heat exchanger before the inlet splitter and after the outlet mixer.
> I upload also a sort of scheme.
> 
> My problem is that: I'm not very expert in modelling HVAC but I'm trying. In the idf I uploaded, there is what I did to realize the nodes connections for the exchanger and the rest of the network, but things are not working correctly.
> 
> Could anyone, try to explain me if and how could I reach my intent?
> 
> Thanks,
> Marco 





__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31782/stime=1398186044>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlMGlqZWk1BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5ODE4NjA0NA-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmNzh0anFlBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTgxODYwNDQ->New Members 7
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkdHRlcTE5BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk4MTg2MDQ0><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___