Re: [EnergyPlus_Support] Plug Loads



Use Electric Equipment under Internal gains object as given below. You can define your own fraction radiant and latent based on requirement..
ElectricEquipment,
    SPACE1-1 ElecEq 1,       !- Name
    SPACE1-1,                !- Zone or ZoneList Name
    EQUIP-1,                 !- Schedule Name
    EquipmentLevel,          !- Design Level Calculation Method
    1056,                    !- Design Level {W}
    ,                        !- Watts per Zone Floor Area {W/m2}
    ,                        !- Watts per Person {W/person}
    0,                       !- Fraction Latent
    0.58,                    !- Fraction Radiant
    0;                       !- Fraction Lost

On Mon, Apr 28, 2014 at 12:18 PM, Fakeha Sehar <<mailto:fakeha_s@xxxxxxxxx>fakeha_s@xxxxxxxxx> wrote:
>  
> So electric plug loads like copiers, printers, fax machines, laptop, task lights can be modeled? Is there any example idf file available?
 On Sunday, April 27, 2014 10:22 AM, "<mailto:dru.crawley@xxxxxxxxxxx>dru.crawley@xxxxxxxxxxx" <<mailto:dru.crawley@xxxxxxxxxxx>dru.crawley@xxxxxxxxxxx> wrote:
> You can model electric, gas and other types and describe sensible and latent heat gains and losses.
> 
> -------- Original message --------
> From: Karen Walkerman
> Date:2014/04/27 1:36 AM (GMT-05:00)
> To: <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx
> Subject: Re: [EnergyPlus_Support] Plug Loads
> 
> 
> 
> Yep
> 
> On Apr 26, 2014 10:56 PM, "Fakeha Sehar" <<mailto:fakeha_s@xxxxxxxxx>fakeha_s@xxxxxxxxx<mailto:<mailto:fakeha_s@xxxxxxxxx>fakeha_s@xxxxxxxxx>> wrote:
> 
> 
> Hi,
> 
> Can plug loads (office equipment) be modeled in EnergyPlus?
> 
> Regards
> 
> 
> 
> 
> ------------------------------------
> 
> Primary EnergyPlus support is found at:
> <http://energyplus.helpserve.com/>> http://energyplus.helpserve.com or send a message to <mailto:energyplus-support@xxxxxxxx>energyplus-support@xxxxxxxx
> 
> The primary EnergyPlus web site is found at:
> <http://www.energyplus.gov/>> http://www.energyplus.gov
> 
> The group web site is:
> <http://groups.yahoo.com/group/EnergyPlus_Support/>> http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.
> 
> EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
> Yahoo Groups Links
> 
> <*> To visit your group on the web, go to:
>     <http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/
> 
> <*> Your email settings:
>     Individual Email | Traditional
> 
> <*> To change settings online go to:
>     <http://groups.yahoo.com/group/EnergyPlus_Support/join>http://groups.yahoo.com/group/EnergyPlus_Support/join
>     (Yahoo! ID required)
> 
> <*> To change settings via email:
>     <mailto:EnergyPlus_Support-digest@xxxxxxxxxxxxxxx>EnergyPlus_Support-digest@xxxxxxxxxxxxxxx
>     <mailto:EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx>EnergyPlus_Support-fullfeatured@xxxxxxxxxxxxxxx
> 
> <*> To unsubscribe from this group, send an email to:
>     <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx>EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx
> 
> <*> Your use of Yahoo Groups is subject to:
>     <https://info.yahoo.com/legal/us/yahoo/utos/terms/>https://info.yahoo.com/legal/us/yahoo/utos/terms/
> 
> 
> 
> 




--


Javed Iqbal, LEED AP, CEA
Sr. Energy Analyst 






__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31820/stime=1398705893>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlYmkzMW1zBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5ODcwNTg5Mw-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmMmNtMmxnBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTg3MDU4OTM->New Members 8
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkdmZjamM0BF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk4NzA1ODkz><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___