[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [EnergyPlus_Support] Problem with UpdateZoneSizing: Heating supply air temperature




On Wednesday, April 30, 2014 11:35 PM, "jeannieboef@xxxxxxxxx" <jeannieboef@xxxxxxxxx> wrote:

Without looking at the attatchments, I suspect that you have not set the (I think third field) sizing:system object to  size by ventilation rate instead of sensible load.

Mit freundlichen GrüÃ?en- Sent from my iPhone (excuse the brevity)
i. A.
Jean Marais
b.i.g. bechtold
Tel.   +49 30 6706662-23
On 30.04.2014, at 23:02, <<mailto:m.aldegheri@xxxxxxxxx>m.aldegheri@xxxxxxxxx> wrote:

>  
Dear all,
> 
> I'm having some trouble with a simulation.
> 
> In my idf, the HVAC system is composed of 2 different entities: a radiant low temperature heating system and a mechanical ventilation system which should provide only a defined air change in my zones. Each of them works only during winter time.
> 
> I upload the .svg to show how the system is realized. In particolar, my mec vent system is not properly a heating system, it provides an only airflow but with a control on the temperature. Just before the entrance of the air flux in a zone, there is a heating coil which should increase the incoming air temperature until 18°C, if the outside air temperature is less than 18°C. If the outside air temperature is >18°C the air flux is not heated by this coil. I should have set this using SetpointManager:OutdoorAirReset,
> 
> SetpointManager:OutdoorAirReset,
>     Air Loop Setpoint Manager,  !- Name
>     Temperature,             !- Control Variable
>     18.00,                   !- Setpoint at Outdoor Low Temperature {C}
>     -20.00,                  !- Outdoor Low Temperature {C}
>     18.00,                   !- Setpoint at Outdoor High Temperature {C}
>     18.00,                   !- Outdoor High Temperature {C}
>     Air Loop Setpoint Manager Node List;  !- Setpoint Node or NodeList Namet;
> 
> I would like to ask you if do you mind how to fix this error. I have many severe errors like this one, one error for each thermal zone.
> 
>    ** Severe  ** UpdateZoneSizing: Heating supply air temperature (calculated) within 2C of zone temperature
>    **   ~~~   ** ...check zone thermostat set point and design supply air temperatures
>    **   ~~~   ** ...zone name = P0:P0%A1ZN4B
>    **   ~~~   ** ...design heating load         = 0.00 W
>    **   ~~~   ** ...thermostat set piont temp   = 0.000 C
>    **   ~~~   ** ...zone temperature            = 17.898 C
>    **   ~~~   ** ...supply air temperature      = 18.000 C
>    **   ~~~   ** ...temperature difference      = 0.10230 C
>    **   ~~~   ** ...calculated volume flow rate = 8253.19807 m3/s
>    **   ~~~   ** ...calculated mass flow rate   = 9723.31707 kg/s
> 
> Maybe the problem is in the design supply air temperatures, which I set to 18°C but I don't understand exaclty what's wrong...
> !-   ===========  ALL OBJECTS IN CLASS: SIZING:ZONE ===========
> 
> Sizing:Zone,
>     P0:P0%A1Zn5i,            !- Zone or ZoneList Name
>     SupplyAirTemperature,    !- Zone Cooling Design Supply Air Temperature Input Method
>     14.00,                   !- Zone Cooling Design Supply Air Temperature {C}
>     5.00,                    !- Zone Cooling Design Supply Air Temperature Difference {deltaC}
>     SupplyAirTemperature,    !- Zone Heating Design Supply Air Temperature Input Method
>     18,                      !- Zone Heating Design Supply Air Temperature {C}
>     15.00,                   !- Zone Heating Design Supply Air Temperature Difference {deltaC}
>     0.0090,                  !- Zone Cooling Design Supply Air Humidity Ratio {kgWater/kgDryAir}
>     0.0040,                  !- Zone Heating Design Supply Air Humidity Ratio {kgWater/kgDryAir}
>     P0:P0%A1Zn5i Design Specification Outdoor Air Object,  !- Design Specification Outdoor Air Object Name
>     1.25,                    !- Zone Heating Sizing Factor
>     1.15,                    !- Zone Cooling Sizing Factor
>     DesignDay,               !- Cooling Design Air Flow Method
>     0.000000,                !- Cooling Design Air Flow Rate {m3/s}
>     0.000760,                !- Cooling Minimum Air Flow per Zone Floor Area {m3/s-m2}
>     0.000000,                !- Cooling Minimum Air Flow {m3/s}
>     0.00,                    !- Cooling Minimum Air Flow Fraction
>     DesignDay,               !- Heating Design Air Flow Method
>     0.000000,                !- Heating Design Air Flow Rate {m3/s}
>     0.002030,                !- Heating Maximum Air Flow per Zone Floor Area {m3/s-m2}
>     0.141580,                !- Heating Maximum Air Flow {m3/s}
>     0.30,                    !- Heating Maximum Air Flow Fraction
>     P0:P0%A1Zn5i Design Specification Zone Air Distribution Object;  !- Design Specification Zone Air Distribution Object Name
> 
> Thank you all,
Marco
> 
> <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/attachments/1413256645;_ylc=X3oDMTJxODk3bzFrBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNhdHRhY2htZW50BHNsawN2aWV3T25XZWIEc3RpbWUDMTM5ODg5MTc2MA-->> View attachments on the web
	 <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/messages/31837;_ylc=X3oDMTJxOW9zNm42BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzMxODM3BHNlYwNmdHIEc2xrA3JwbHkEc3RpbWUDMTM5ODg5MTc2MA--?act=reply&messageNum=31837>Reply via web post 	? <mailto:m.aldegheri@xxxxxxxxx?subject=Re%3A%20Problem%20with%20UpdateZoneSizing%3A%20Heating%20supply%20air%20temperature> Reply to sender 	?	 <mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx?subject=Re%3A%20Problem%20with%20UpdateZoneSizing%3A%20Heating%20supply%20air%20temperature> Reply to group 	?	 <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/newtopic;_ylc=X3oDMTJlM3FtNXF0BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA250cGMEc3RpbWUDMTM5ODg5MTc2MA-->Start a New Topic 	?	 <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/conversations/topics/31837;_ylc=X3oDMTM2a3FnaHY5BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BG1zZ0lkAzMxODM3BHNlYwNmdHIEc2xrA3Z0cGMEc3RpbWUDMTM5ODg5MTc2MAR0cGNJZAMzMTgzNw-->Messages in this topic (1)

<https://groups.yahoo.com/neo;_ylc=X3oDMTExc2JuanI3BF9TAzk3MzU5NzE0BGNmMTADQ1AEc2VjA21lZ2FwaG9uZQ-->
Now you can search Photos & Files in your Group !
You can now search not only your archive of conversations, but also photos and files stored in your Yahoo Group. Give it a try!
<http://yahoogroups.tumblr.com/post/79361353100/photo-and-files-search-launched>
> <MRD xlam 30-04 recup dati dimensionamento modif.svg>
> <MRD xlam 30-04 recup dati dimensionamento modif.rar>




__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31839/stime=1398929716>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlM3RxOWZvBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5ODkyOTcxNg-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmcGg0NGtjBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTg5Mjk3MTY->New Members 9
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkbHY3ZHNvBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk4OTI5NzE2><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___