Re: [EnergyPlus_Support] ** Severe ** Too many iterations (SOLVZP) in Airflow Network simulation




Try decrease the simulation timestep.


2014-05-05 13:41 GMT+02:00 <<mailto:m.aldegheri@xxxxxxxxx>m.aldegheri@xxxxxxxxx>:
>  
Hi all,
> I have a problem with the processing of a idf.
> The model have an AFN and it's a nat vent building.
> 
> E+ gives me this fatal error...
> 
>   ** Severe  ** Too many iterations (SOLVZP) in Airflow Network simulation
>    ** Warning ** AirflowNetwork: SOLVER, Changing values for initialization flag, Relative airflow convergence, Absolute airflow convergence, Convergence acceleration limit or Maximum Iteration Number may solve the problem.
>    **   ~~~   **  During Warmup & Sizing, Environment=SUMMER DESIGN DAY IN PALAZZINE ITEA GARDOLO, at Simulation time=07/15 10:30 - 11:00
>    **   ~~~   ** ..Iterations=30000, Max allowed=30000
>    **  Fatal  ** AirflowNetwork: SOLVER, The previous error causes termination.
> 
> At the moment in the idf is set:
> 
> !-   ===========  ALL OBJECTS IN CLASS: AIRFLOWNETWORK:SIMULATIONCONTROL ===========
> 
> AirflowNetwork:SimulationControl,
>     VENT,                    !- Name
>     MultizoneWithoutDistribution,  !- AirflowNetwork Control
>     Input,                   !- Wind Pressure Coefficient Type
>     Cp Data,                 !- AirflowNetwork Wind Pressure Coefficient Array Name
>     OpeningHeight,           !- Height Selection for Local Wind Pressure Calculation
>     LowRise,                 !- Building Type
>     30000,                   !- Maximum Number of Iterations {dimensionless}
>     ZeroNodePressures,       !- Initialization Type
>     0.0001,                  !- Relative Airflow Convergence Tolerance {dimensionless}
>     0.000001,                !- Absolute Airflow Convergence Tolerance {kg/s}
>     -0.5,                    !- Convergence Acceleration Limit {dimensionless}
>     ,                        !- Azimuth Angle of Long Axis of Building {deg}
>     ;                        !- Ratio of Building Width Along Short Axis to Width Along Long Axis
> 
> I tried to change the convergence parameters from
> 
>     0.0001,                  !- Relative Airflow Convergence Tolerance {dimensionless}
>     0.000001,                !- Absolute Airflow Convergence Tolerance {kg/s}
>     -0.5,                    !- Convergence Acceleration Limit {dimensionless}
> 
> to
> 
>     0.01,                  !- Relative Airflow Convergence Tolerance {dimensionless}
>     0.0001,                !- Absolute Airflow Convergence Tolerance {kg/s}
>     -0.5,                    !- Convergence Acceleration Limit {dimensionless}
> 
> but I can't solve the problem.
> I'm not very familiar with these parameters, especially with the last one about which the manuals do not give many informations.
> 
> 
> 




__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31870/stime=1399297450>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlbmh2YWlqBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTM5OTI5NzQ1MA-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmNWRhZzloBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzEzOTkyOTc0NTA->New Members 14
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkNXUyazFwBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxMzk5Mjk3NDUw><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___