Re: [EnergyPlus_Support] ThermostatSetpoint:DualSetpoint heating value not working (?)



If you have an economiser and or a heat exchanger, I would recommend checking the contols. You should monitor when these devices are operating.


2014-05-15 10:51 GMT+02:00 <mailto:lmblanes@xxxxxxxxx>lmblanes@xxxxxxxxx [EnergyPlus_Support] <<mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx>EnergyPlus_Support@xxxxxxxxxxxxxxx>:
>  
Jean
> 
> Thanks for your response.
> 
> Previously, I meant just that the Setpoint was working (apologies for the confusing writing).
> As you pointed, I checked the Air Supply Temperature and Setpoint at the AirLoopSupplySideOutlet1 and the SP temperature is not reached in Winter. (In Summer the SP is reached mostly during the day, (but not during evening and nightime). I attached another two graphs to show this.
> 
> Winter and Summer Design Days are used for sizing calculations. I fixed some parameters in the sizing objects (temperature of supply air etc) that were not right, but still shows the same issue.
> 
> Thanks
> 
> Luis, from Hibernia.





__._,_.___

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31945/stime=1400144561>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlZWRrYXI5BF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQwMDE0NDU2MQ-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmNW9xNmJtBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0MDAxNDQ1NjE->New Members 6
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkNzI2cW1rBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDAwMTQ0NTYx><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___