[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

[EnergyPlus_Support] Window frame conductance form EU U-Value



Hi all,
Here is my problem:
To derive the frame conductance input for EnergyPlus from a frame U-Value calculated based on ISO 10077 (for example 1.4 W/m2.K), I guess it is correct that I only strip off the assumed air film resistance values (0.04 for outdoor and 0.13 for indoor) like this:
h = 1 / ( 1/1.4 - 0.04 - 0.13) = 1.84 W/m2.K
Am I right?
What makes me skeptical is that I read in one DesignBuilder forum that one also needs to consider the boundary condition temperature assumptions in NRC-100 (-18 and 21) and ISO 10077 (0 and 20) like this:

h = 1.84 * (21-(-18)) / (20-0) = 3.59 W/m2.K
But, to me this second step does not make sense. Because, as far as I know, the U value is presented based on 1K temperature difference in both methods.
Do you have any idea on this question?
Best,
Farhang Tahmasebi



__._,_.___

 Posted by: farhang.tahmasebi@xxxxxxxxx

Primary EnergyPlus support is found at:
<http://energyplus.helpserve.com>http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
<http://www.energyplus.gov>http://www.energyplus.gov

The group web site is:
<http://groups.yahoo.com/group/EnergyPlus_Support/>http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.


<http://geo.yahoo.com/serv?s=97476590/grpId=3387488/grpspId=1705007389/msgId=31971/stime=1400678830>

<https://groups.yahoo.com/neo/groups/EnergyPlus_Support/info;_ylc=X3oDMTJlOWtlNGUxBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZnaHAEc3RpbWUDMTQwMDY3ODgzMA-->Visit Your Group
* <https://groups.yahoo.com/neo/groups/EnergyPlus_Support/members/all;_ylc=X3oDMTJmNDNlcmNtBF9TAzk3MzU5NzE0BGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwN2dGwEc2xrA3ZtYnJzBHN0aW1lAzE0MDA2Nzg4MzA->New Members 8
<https://groups.yahoo.com/neo;_ylc=X3oDMTJkamNva2xpBF9TAzk3NDc2NTkwBGdycElkAzMzODc0ODgEZ3Jwc3BJZAMxNzA1MDA3Mzg5BHNlYwNmdHIEc2xrA2dmcARzdGltZQMxNDAwNjc4ODMw><http://l.yimg.com/ru/static/images/yg/img/email/new_logo/logo-groups-137x15.png>
? <https://info.yahoo.com/privacy/us/yahoo/groups/details.html>Privacy ? <mailto:EnergyPlus_Support-unsubscribe@xxxxxxxxxxxxxxx?subject=Unsubscribe>Unsubscribe ? <https://info.yahoo.com/legal/us/yahoo/utos/terms/>Terms of Use
__,_._,___