Julien, It sounds as though the natural drift / convection is causing enough cooling to reduce your outlet temperature to 5C. Assuming there is actually some load, I think that turning off a couple of towers may help. If there I no load, there may be no difference. Also, 900 errors in a complete annual simulation doesn’t sound like much to worry about. Finally, the “Max = 5, Min = 5” text doesn’t make much sense to me unless you’ve defined the maximum loop temp to be 5C. If so, consider making the max = 15. James V Dirkes II, PE, BEMP, LEED AP www.buildingperformanceteam.com Energy Analysis, Commissioning & Training Services 1631 Acacia Drive, Grand Rapids, MI 49504 USA 616 450 8653 From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Sent: Tuesday, July 08, 2014 6:54 AM To: EnergyPlus_Support@xxxxxxxxxxxxxxx Subject: [EnergyPlus_Support] Cooling Tower outlet temperature below specified minimum Hi,
I've got a building with 4 cooling towers and a big cooling load all year, including the winter. I'm getting the following errors (Here for one week only, in january)
************* ** Warning ** CoolingTower:VariableSpeed "COOLING TOWER 1" Cooling tower water outlet temperature is below the specified minimum condenser loop temp error continues... ************* ** ~~~ ** This error occurred 909 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=5. Min=5. ************* ************* ** Warning ** CoolingTower:VariableSpeed "COOLING TOWER 2" Cooling tower water outlet temperature is below the specified minimum condenser loop temp error continues... ************* ** ~~~ ** This error occurred 909 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=5. Min=5. ************* ************* ** Warning ** CoolingTower:VariableSpeed "COOLING TOWER 3" Cooling tower water outlet temperature is below the specified minimum condenser loop temp error continues... ************* ** ~~~ ** This error occurred 909 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=5. Min=5. ************* ************* ** Warning ** CoolingTower:VariableSpeed "COOLING TOWER 4" Cooling tower water outlet temperature is below the specified minimum condenser loop temp error continues... ************* ** ~~~ ** This error occurred 67 total times; ************* ** ~~~ ** during Warmup 0 times; ************* ** ~~~ ** during Sizing 0 times. ************* ** ~~~ ** Max=5. Min=5.
My minimum condenser loop temperature is 5C. I also have a basin heater set at 2°C. Here it seems that I'm getting all these warnings (they're only for one week in January...) without much cause since Max=5. and Min=5. Can I discard them?
Also, I'm wondering if I shouldn't just turn off 1 or 2 CTs when outside temperature is below 5°C or something like that, so I'd be closer to the needed capacity. Does that make any sense to you? If I were to do this, should I use the "PlantEquipmentOperation:OutdoorDryBulb" object or is there a better way to do it? I've tried doing it as follows and it made things worse, temperature was below setpoint 2671 times for each tower (which I don't even understand since I'm simulating 24*7*6=1008 timesteps...) :
CondenserEquipmentList, Chiller 1_TowerWaterSys Equipment List, !- Name COOLINGTOWER:VARIABLESPEED, !- Equipment 1 Object Type cooling tower 1, !- Equipment 1 Name COOLINGTOWER:VARIABLESPEED, !- Equipment 2 Object Type cooling tower 2, !- Equipment 2 Name COOLINGTOWER:VARIABLESPEED, !- Equipment 3 Object Type cooling tower 3, !- Equipment 3 Name COOLINGTOWER:VARIABLESPEED, !- Equipment 4 Object Type cooling tower 4; !- Equipment 4 Name
CondenserEquipmentList, Chiller 1_TowerWaterSys Equipment List 1-2 ON, !- Name COOLINGTOWER:VARIABLESPEED, !- Equipment 1 Object Type cooling tower 1, !- Equipment 1 Name COOLINGTOWER:VARIABLESPEED, !- Equipment 2 Object Type cooling tower 2; !- Equipment 2 Name
PlantEquipmentOperation:OutdoorDryBulb, CT two off below 10C, !- Name -70, !- Dry-Bulb Temperature Range 1 Lower Limit {C} 10, !- Dry-Bulb Temperature Range 1 Upper Limit {C} Chiller 1_TowerWaterSys Equipment List 1-2 ON, !- Range 1 Equipment List Name 10, !- Dry-Bulb Temperature Range 2 Lower Limit {C} 70, !- Dry-Bulb Temperature Range 2 Upper Limit {C} Chiller 1_TowerWaterSys Equipment List; !- Range 2 Equipment List Name
CondenserEquipmentOperationSchemes, Chiller 1_TowerWaterSys Loop Operation Scheme List, !- Name PlantEquipmentOperation:OutdoorDryBulb, !- Control Scheme 1 Object Type CT two off below 10C, !- Control Scheme 1 Name PlantOnSched; !- Control Scheme 1 Schedule Name
(plantOnSched = 1 all times) Thanks for any help you can provide, Best,
__._,_.___
Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx>
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___
|