Hi Joe. Some info that is somewhat related (shading rather than reflectance effects) is:

 

http://www.fsec.ucf.edu/en/publications/html/FSEC-PF-302-96/ (also published as a 2002 ACEEE Summer Study paper)

 

-Craig

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Saturday, July 19, 2014 19:38
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: Re: [EnergyPlus_Support] Rooftop outdoor air temperatures

 

 

Craig,

Thanks for circulating this report, which goes a long ways in answering the question of how much do the air temperatures above a roof change when the roof reflectance changes (answer seems to be very little, around 0.3 C). Has anyone also looked into the impact of the increased solar gain on the AHU due to more reflected solar from the roof ?  This reminds me of the conversation I had with a colleague at an ASHRAE conference two years ago, who thought that increasing the albedo of streets and pavement might actually increase rather than decrease thermal discomfort of pedestrians due to the increased reflected solar, as well as visual discomfort.

Joe

Joe Huang
White Box Technologies, Inc.
346 Rheem Blvd., Suite 108D
Moraga CA 94556
yjhuang@xxxxxxxxxxxxxxxxxxxxxxxx
http://weather.whiteboxtechnologies.com for simulation-ready weather data
(o) (925)388-0265
(c) (510)928-2683
"building energy simulations at your fingertips"


On 7/19/2014 11:39 AM, Craig Wray CPWray@xxxxxxx [EnergyPlus_Support] wrote:

 

There is indeed some related research on the effects of roof reflectance on air temperatures near rooftop condensing units. See:

 

http://heatisland.lbl.gov/publications/effects-roof-reflectance-air-temperatures-surrounding-rooftop-condensing-unit

 

Regards, Craig Wray

 

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Saturday, July 19, 2014 10:38
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Rooftop outdoor air temperatures

 

 

Dear Forum,

I have had clients in the past who refused to place HVAC equipment on the roof in Dallas, Texas because they knew the near-roof temperatures were much warmer than the temperature farther away.  The situations have been for large, black roofs which get very warm in the summer.

I have not thought about that much for energy models other than defining high SRI roofing materials.  Yesterday, however, I was talking to an infrared thermal imaging professional who says that he has measured roof temperatures that were 100F / 56C higher(!) than the nominal outdoor temperature.  If that is true, then all of my energy calculations for rooftop equipment are WRONG � not a happy thought for someone who wants results thatt are realistic.

The resulting questions to the most knowledgeable modeling community in the world (as far as I can tell) are:

·         Are you aware of research which has measured or characterized near-roof temperatures?

·         Do you have a modeling practice that accounts for the near-roof impact on outdoor air intakes or roof-mounted chillers, condensing units or cooling towers?

 

Thanks in advance for your insights!

 

James V Dirkes II, PE, BEMP, LEED AP
www.buildingperformanceteam.com
Energy Analysis, Commissioning & Training Services
1631 Acacia Drive, Grand Rapids, MI 49504 USA
616 450 8653

 

From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
Sent: Friday, July 18, 2014 3:37 PM
To: EnergyPlus_Support@xxxxxxxxxxxxxxx
Subject: [EnergyPlus_Support] Re: Curve Fit Tool

 

 

Thank you very much for you help

 

Kind Regards,

 

Felipe Durán



__._,_.___

Posted by: Craig Wray <cpwray@xxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.





__,_._,___