|
Hisham, The value is a judgment on the part of the energy modeler and should reflect realistic expectations for the HVAC system control. I like to use 0.5C, although I think you can justify up to 1C, depending on the system. The E+ default value is too small, in my opinion, for almost every system and can produce large numbers of unmet heating / cooling load hours. James V Dirkes II, PE, BEMP, LEED AP From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx] Dear group, Please, can anyone define exactly where to get this value? Default OutputControl:ReportingTolerances is 0.2C in e+ and 0.5C in DB, I searched the group but no posts defined this clearly. If there is some procedure to determine this tolerance for each certain project, then please describe it. Hisham __._,_.___ Posted by: Jim Dirkes <jim@xxxxxxxxxxxxxxxxxxxxxxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |