Re: [EnergyPlus_Support] Air Humidity Ratio





Hi,

You could have a problem in your model.

But it could be that you're just misreading the results. Did you request "Zone Air Relative Humidity" or "Zone Air Humidity Ratio"?

The former outputs Rh in %, the latter outputs kgWater/kgDryAir and will show very low values, typically below 0.01 that you might have mistaked for "under 1% RH".


If you're reading the results right, you could send your model, I'll try to take a look at what's wrong when I've a bit of free time.

Best,
Julien


--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13

LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr



2014-08-17 13:15 GMT+02:00 myesta205@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

HiI want to have zone humidity ratio with EP.

My whether data humidity ratio is 30-60 %in each the year. But EP output give me the zone Air Humidity Ratio under 1% in each day!!!.

I think there is a problem with my model or Energyplus cant calculate this topic.

How can I solve my problem?

thanks

 




__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___