|
Well for anyone interested, I’ll answer my own question. The Reference building models autosize the mechanical system on the design files. This includes the sensible heat ratio of the cooling coils. For some areas
of the country, the max dehumidification load does not correspond to the summer design temperature. When EnergyPlus calculates the cooling coil output, it apparently can’t or doesn’t resolve air conditions that exceed the sensible hear ratio. All that was
necessary to fix the RH exceeding 100% errors was to round up the autosize sensible heat ratios to the next larger two digit value and enter them manually and then let E+ autosize the rest of the system. Ned Lyon, P.E. (MA, WV) SIMPSON GUMPERTZ & HEGER
From: EnergyPlus_Support@xxxxxxxxxxxxxxx [mailto:EnergyPlus_Support@xxxxxxxxxxxxxxx]
I’m trying to help a colleague with a version 7.2 PsyRhFnTdbWPb Relative Humidity out of range error. We are running a DOE Commercial Reference Building and modifying the envelope,
windows and locations. All the mechanical are autosized. When this building is run in Chicago, we have RH out of range errors. We do not have these errors in other locations. Can anyone suggest a way to mitigate these errors. Shorter time steps and more
HVAC iterations do not help. Oversizing cooling by 2.8 does work, but I’m not sure that is the best plan. Thanks in advance. Ned Lyon, P.E. (MA, WV) 781.907.9000 main __._,_.___ Posted by: "Edward G. Lyon" <EGLyon@xxxxxxx> Primary EnergyPlus support is found at: http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx The primary EnergyPlus web site is found at: http://www.energyplus.gov The group web site is: http://groups.yahoo.com/group/EnergyPlus_Support/ Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files. EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button. __,_._,___ |