Re: [EnergyPlus_Support] Control of HVAC operation depending on Outdoor Temperature





Marcos,

I think you should look up "AvailabilityManager:HighTemperatureTurnOff" in the E+ I/O manual, in order to shut off the HW loop (it will shut off the pump)

You'll probably need an OutdoorAir:Node
Referenced in AvailabilityManager:HighTemperatureTurnOff
Refererenced in AvailabilityManagerAssignmentList
Refererenced in  PlantLoop


Hope this helps,
Julien

(PS: that if it was a condenser loop, you could do it in a simpler way with PlantEquipmentOperation:OutdoorDrybulb)



--
Julien Marrec, EBCP, BPI MFBA
Energy&Sustainability Engineer
T: +33 6 95 14 42 13

LinkedIn (en) : www.linkedin.com/in/julienmarrec
LinkedIn (fr) : www.linkedin.com/in/julienmarrec/fr



2014-09-01 8:36 GMT+02:00 marcusbrown1326@xxxxxxxxx [EnergyPlus_Support] <EnergyPlus_Support@xxxxxxxxxxxxxxx>:
 

Hi all, 


I'm using HVACTemplate: Zone: FanCoil in my simulations and I need to control the hours of operations of the HVAC system depending upon the outdoor air temperature. For example, if the outdoor temperature is lower than 25 degrees, the Cooling should be turned off.


I wonder if it is possible to implement this kind of control only with HVAC templates and if possible, how to do it.


Thanks so much in advance!


Marcos Perez-Vazquez




__._,_.___

Posted by: Julien Marrec <julien.marrec@xxxxxxxxx>


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
• Privacy • Unsubscribe • Terms of Use

__,_._,___