[EnergyPlus_Support] Autosizing of heating coil UA failed





Dear forum,


I have a severe error in my model and I am not able to find the problem. Here is the error:


  ** Severe  ** Autosizing of heating coil UA failed for Coil:Heating:Water "name of zone" FAN COIL UNIT HEATING COIL

 **   ~~~   **   Bad starting values for UA

   **   ~~~   **   Lower UA estimate = 351.326817 W/m2-K (0.1% of Design Coil Load)

   **   ~~~   **   Upper UA estimate = 351326.817985 W/m2-K (100% of Design Coil Load)

   **   ~~~   **   Zone "N00MB:PHYSCLMDCNAHU27" coil sizing conditions (may be different than Sizing inputs):

   **   ~~~   **   Coil inlet air temperature     = 98.627 C

   **   ~~~   **   Coil inlet air humidity ratio  = 3.974E-003 kgWater/kgDryAir

   **   ~~~   **   Coil inlet air mass flow rate  = 20.768964 kg/s

   **   ~~~   **   Design Coil Capacity           = -373993.539 W

   **   ~~~   **   Design Coil Load               = 351326.817 W

   **   ~~~   **   Inadequate water side capacity: in Plant Sizing for this hot water loop

   **   ~~~   **   increase design loop exit temperature and/or decrease design loop delta T

   **   ~~~   **   Plant Sizing object = HW LOOP

   **   ~~~   **   Plant design loop exit temperature = 80.000 C

   **   ~~~   **   Plant design loop delta T          = 10.000 C

   **  Fatal  ** Preceding water coil sizing errors cause program termination


I am modeling an HVAC system that uses the zoneHVAC:FourPipeFanCoil object, connected to an air cooled chiller. I have several zones connected and only one of them has this severe error, and I have checked the IDF file and have not found any inconsistency in the corresponding data of this particular zone. 


Any help would be greatly appreciated,


Regards,

Santiago




__._,_.___

Posted by: iluminasol33@xxxxxxxxx


Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx

The primary EnergyPlus web site is found at:
http://www.energyplus.gov

The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/

Attachments are currently allowed but be mindful that not everyone has a high speed connection.  Limit attachments to small files.

EnergyPlus Documentation is searchable.  Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.




Visit Your Group
Yahoo! Groups
PrivacyUnsubscribeTerms of Use

__,_._,___