[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]
[EnergyPlus_Support] Autosizing of heating coil UA failed
- To: <EnergyPlus_Support@xxxxxxxxxxxxxxx>
- Subject: [EnergyPlus_Support] Autosizing of heating coil UA failed
- From: "iluminasol33@xxxxxxxxx [EnergyPlus_Support]" <EnergyPlus_Support@xxxxxxxxxxxxxxx>
- Date: 07 Oct 2014 13:58:02 -0700
- Delivered-to: mailing list EnergyPlus_Support@xxxxxxxxxxxxxxx
- Delivery-date: Tue, 07 Oct 2014 14:58:12 -0600
- Dkim-signature: v=1; a=rsa-sha256; c=relaxed/relaxed; d=yahoogroups.com; s=echoe; t=1412715483; bh=gFzl2zLW4QCxrgWzY+b5AsR+gaUniy/39irF9bKh0VA=; h=Received:Received:X-Yahoo-Newman-Id:X-Sender:X-Apparently-To:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:X-Received:To:Message-ID:X-Mailer:X-Original-From:X-Originating-IP:X-Yahoo-Post-IP:From:X-Yahoo-Profile:Sender:MIME-Version:Mailing-List:Delivered-To:List-Id:Precedence:List-Unsubscribe:Date:Subject:Reply-To:X-Yahoo-Newman-Property:Content-Type:From:Subject; b=pkX9mT+uEQeU+er3WRO14qEs2AdE9GXRtFtuMPTV1S3ZbNL1rTpl06gqOvwOeQtl0htHjYFG1Gk9hPJgFrkbVJ24ZWDg5GJjQfzMIBH4UHv7cUBOANbuStrxyu5arwAfOc8e1AzVpx1Y0wWf8mhDKVqP7RPiJF0pqTIduqkh8Dg=
- Domainkey-signature: a=rsa-sha1; q=dns; c=nofws; s=echoe; d=yahoogroups.com; b=rRxByGeSzye0RJ2/uj+/E+gsK2bY/hi6X6DkZowhroOFanmaAqUnePEqvGyyLstQlQCbyaLjJcuiSsu0TlKqu0AN7HSi9uGwbgFwJS77umlRIBVh9LujhYTF2Yk2cC6Jdx8eelO4eSZSOQAeIIlwtCIL046lCa4GVg+fd5dlySU=;
- Envelope-to: linda@xxxxxxxxxxxxxx
- List-id: <EnergyPlus_Support.yahoogroups.com>
- List-unsubscribe: <mailto:EnergyPlus_Support-unsubscribe@yahoogroups.com>
- Mailing-list: list EnergyPlus_Support@xxxxxxxxxxxxxxx; contact EnergyPlus_Support-owner@xxxxxxxxxxxxxxx
- Reply-to: EnergyPlus_Support@xxxxxxxxxxxxxxx
Dear forum,
I have a severe error in my model and I am not able to find the problem. Here is the error:
** Severe ** Autosizing of heating coil UA failed for Coil:Heating:Water "name of zone" FAN COIL UNIT HEATING COIL
** ~~~ ** Bad starting values for UA
** ~~~ ** Lower UA estimate = 351.326817 W/m2-K (0.1% of Design Coil Load)
** ~~~ ** Upper UA estimate = 351326.817985 W/m2-K (100% of Design Coil Load)
** ~~~ ** Zone "N00MB:PHYSCLMDCNAHU27" coil sizing conditions (may be different than Sizing inputs):
** ~~~ ** Coil inlet air temperature = 98.627 C
** ~~~ ** Coil inlet air humidity ratio = 3.974E-003 kgWater/kgDryAir
** ~~~ ** Coil inlet air mass flow rate = 20.768964 kg/s
** ~~~ ** Design Coil Capacity = -373993.539 W
** ~~~ ** Design Coil Load = 351326.817 W
** ~~~ ** Inadequate water side capacity: in Plant Sizing for this hot water loop
** ~~~ ** increase design loop exit temperature and/or decrease design loop delta T
** ~~~ ** Plant Sizing object = HW LOOP
** ~~~ ** Plant design loop exit temperature = 80.000 C
** ~~~ ** Plant design loop delta T = 10.000 C
** Fatal ** Preceding water coil sizing errors cause program termination
I am modeling an HVAC system that uses the zoneHVAC:FourPipeFanCoil object, connected to an air cooled chiller. I have several zones connected and only one of them has this severe error, and I have checked the IDF file and have not found any inconsistency in the corresponding data of this particular zone.
Any help would be greatly appreciated,
Regards,
Santiago
__._,_.___
Posted by: iluminasol33@xxxxxxxxx
Primary EnergyPlus support is found at:
http://energyplus.helpserve.com or send a message to energyplus-support@xxxxxxxx
The primary EnergyPlus web site is found at:
http://www.energyplus.gov
The group web site is:
http://groups.yahoo.com/group/EnergyPlus_Support/
Attachments are currently allowed but be mindful that not everyone has a high speed connection. Limit attachments to small files.
EnergyPlus Documentation is searchable. Open EPlusMainMenu.pdf under the Documentation link and press the "search" button.
__,_._,___